Hi,
I’m trying to find out if I should have 2 strings or 4. I will have 12 panels on an east facing roof and 12 on the west.
I will be using Longi 430w panels and a Sunsynk 8.8kw inverter.
The DataSheet for the inverter states a maximum DC voltage of 500v and the datasheet for the panels states a Voc of 39v (12x39=469v) so I’m within the limits if I use 2 strings.
However 469v takes me outside the MPPT tracking range.
When calculating the voltage from the array for the MPPT should I be using Voc or Vmp? If I use the Vmp of 33v x 12 it gives me 396v which is nicely inside the range.
I have been advised by one person to use 4 strings because it’s safer for the inverter but I have also beefed advised to use 2 strings because the higher voltages help with efficiency.
Thanks