The lines need a DC path to ground, to prevent the atmosphere's about 100v/meter vertical field from charging up the lines, as they run over hills or higher, to voltages that would arc over and damage equipment. So to a first approximation the typical long-haul transmission line is fed by three transformers in a Y configuration, with the center joint grounded. You have to ground it at both/all ends, so you don't have it "floating" when the breakers are open. So the three wires as a group act like a single long wire (see "phantom circuit") and the connection to the local ground at the ends completes the circuit.
Are you saying that transformers for high voltage transmission use Y configuration for both the secondary step-up driving the line and primary of step-down being driven? Unlike Y secondary and Delta primary for most low-voltage applications? Because it needs to drain off high voltage low current which is developed, to avoid breakdown of insulation?
The solution is to put something in those connections between the Y center and the local ground. A resistor to limit DC / low-frequency induced currents, maybe bypassed with a big capacitor to keep things running smoothly when the phases aren't balanced or one line has a fault, a current detector that fast-trips the disconnect, etc. These are big and pricey.
Seems to me a resistor would either allow the current anyway, or limit current but allow excessive voltage. So disconnect would be the only way.