I like 3% for the calculator, then step up one size on the cable.What does everyone on here consider a max acceptable voltage loss for your DC cables?
Consider what the loss actually is, generated heat.What does everyone on here consider a max acceptable voltage loss for your DC cables?
That translates to about 0.0072 ohms. ( I think) That is about 7' of #10 wire.Consider what the loss actually is, generated heat.
If you have 48V and 200A = 9600W
3% of this is 288W
That’s roughly 10x little soldering irons.
Do the math and calculate the loss/waste/heat with your setup.
I was looking at putting my array about 170 ft from my controller. But voltage would be high, around 412 voc and only 10 amps with 6awg wireThat translates to about 0.0072 ohms. ( I think) That is about 7' of #10 wire.
a 3/0 wire has about 62uohms/ft This translates to about 112' round trip for 3% losses. Check my math please. I am not a mathematician.
In any case the wire needs to be sized for FLA.
I was looking at putting my array about 170 ft from my controller. But voltage would be high, around 412 voc and only 10 amps with 6awg wire
Need vmpI was looking at putting my array about 170 ft from my controller. But voltage would be high, around 412 voc and only 10 amps with 6awg wire
344.7Need vmp
14 gauge would put you at 2.93% voltage drop.344.7
Just messing with numbers... 50W better for a year...Much better.
Less than 50w loss.
I have some 6 gauge that i was going to use14 gauge would put you at 2.93% voltage drop.
But, I wouldn't recommend anything less than 10 awg.
344v
10a
170ft
Even betterI have some 6 gauge that i was going to use