So I got the cheapest 24V 100AH battery on Aliexpress that is in stock in Europe to make a small secondary system(replacing lead). Sadly I discovered a video by a Russian guy who bought a 600wh power station from the same brand and discovered it is actually 300wh. So I didn't have high hopes.
Still I decided to test it fully.
The battery arrived almost fully charged, which was very strange as they should not be stored for a long time like this. The voltage read 26.9V. It took about 5 minutes at 30A to charge to 3.6V. Then once the voltage settled to about 28V I tried 1.3kW load through the inverter (the inverter is well tested) and the voltage at 100A dropped to 22V at the battery terminals! 6V at 100A! That's like 60mOhm. It should be 10 times less.
So then I charged it up with a PSU. This time to 3.6V per cell (wanting to avoid high voltage cutoff at 3.65V) and the plan was to check capacity with my 185W load tester. I'd love to be able to do proper 0.2C discharge, but at this voltage the best it can do is 6A.
It also shows the internal resistance of the battery. Which it initially showed at about 20mOhm growing to 150mOhm within minutes.... At 6A!?!
I'm not sure I'll wait the 16h it takes to complete the test. I might charge it up again and discharge with a known load through the inverter so I can send it back sooner rather than later.
My question is, has anyone else encountered this? I expect half the size, but not internal resistance worse than my old lead acid...tue weight is correct. The price is lie, but not outrageous... Also reviews are good. So, I don't know what to make of it.
Edit: Also I asked the seller to send me the battery spec sheet and it says internal resistance <= 500mOhm WTF?! Is this common? In this case it is certainly within spec... But at the same time it says max continuous discharge 100A and max surge 200A.
Still I decided to test it fully.
The battery arrived almost fully charged, which was very strange as they should not be stored for a long time like this. The voltage read 26.9V. It took about 5 minutes at 30A to charge to 3.6V. Then once the voltage settled to about 28V I tried 1.3kW load through the inverter (the inverter is well tested) and the voltage at 100A dropped to 22V at the battery terminals! 6V at 100A! That's like 60mOhm. It should be 10 times less.
So then I charged it up with a PSU. This time to 3.6V per cell (wanting to avoid high voltage cutoff at 3.65V) and the plan was to check capacity with my 185W load tester. I'd love to be able to do proper 0.2C discharge, but at this voltage the best it can do is 6A.
It also shows the internal resistance of the battery. Which it initially showed at about 20mOhm growing to 150mOhm within minutes.... At 6A!?!
I'm not sure I'll wait the 16h it takes to complete the test. I might charge it up again and discharge with a known load through the inverter so I can send it back sooner rather than later.
My question is, has anyone else encountered this? I expect half the size, but not internal resistance worse than my old lead acid...tue weight is correct. The price is lie, but not outrageous... Also reviews are good. So, I don't know what to make of it.
Edit: Also I asked the seller to send me the battery spec sheet and it says internal resistance <= 500mOhm WTF?! Is this common? In this case it is certainly within spec... But at the same time it says max continuous discharge 100A and max surge 200A.