Is that why you spent way more than 10 minutes argueing about it on the internet?
 
They aren't talking about using a busbar in the manual, they are talking about direct connections from a battery or batteries to an inverter or inverters,


So the way I am using the busbars is a different case than what the manual is referring to. I would have thought that Sunshine_Eggo would have known that.
IMG_1458.jpeg

That’s odd

So not only does it talk about bus bars, but also says you’re using the wrong wire size (ya know, since we’re being “technical” now)
 
This is the cable:


5.94mm diameter.

Doesn't compute, the link is for cable 9.4mm in diameter.

You can't put the Lynx Power In in a different place, its bus bars literally bolt onto the Lynx Distributor's bus bars, so they have to be side by side.

You can put the second Lynx anywhere. It only requires cables from one to the other. You do not have to bolt the 2 together. I own a Lynx, I find the busbar sticking out the side to be useless in my application. Maybe I'll add some more batteries and use them but really, I would have just like a bigger enclosure with all terminal connections under it.

I didn't notice the load differences on the video, I will have a closer look.
Look closely, it is all through the video.

The video was made for marketing purposes and not necessarily by a knowledgeable person. As such, technical details such as equal cable length are overlooked. Don't always follow what you see in marketing material, it may not always be correct.
 
I would put the two units close to each other on the left and then hang the power-in over on the right at the same level.

No big deal though, just preference.

Hopefully you at least report to tell us if the cable length causes issues.

How cool is it that Tim's electric knew right away that you were Euro and 230 and thus your units are parallel and that is the exact operating setup where cable length is most critical.

Pretty neat that some random guy here across the pond on an internet forum knew that right away.
 
I would put the two units close to each other on the left and then hang the power-in over on the right at the same level.

No big deal though, just preference.

Hopefully you at least report to tell us if the cable length causes issues.

How cool is it that Tim's electric knew right away that you were Euro and 230 and thus your units are parallel and that is the exact operating setup where cable length is most critical.

Pretty neat that some random guy here across the pond on an internet forum knew that right away.
@timselectric is an idiot though what are you on about





/sarcasm
 
Last edited:
Is that why you spent way more than 10 minutes argueing about it on the internet?
Does that negate what I just said? We'll see what the result is when it's all set up later this week. I prefer talking about facts, actual figures, not vague 'You might have problems' and the like. Still waiting for timselectric to tell us what size cables he had a problem with on his set up. I wonder why he isn't telling us.
 
One thing Tim is right about, these are 230V Euro inverters in parallel and one inverter will probably carry more load due to any slight difference in supply voltage. If you watch that video closely, you will see the load on the slave inverter is less than 1/2 of the load on the master, if in parallel it should be equal. This is important as you will hit peak 5Kw output sooner on one inverter under heavy loads and instead of 10Kw, you may only have 7.5Kw load capacity before the inverter with higher load shuts down.

Can you give me a timestamp for where you see the loads on the inverters are different?
 
Can you give me a timestamp for where you see the loads on the inverters are different?
Left inverter shows 50.0V in big numbers in the center, he then moves to the right and it shows 49.8V.

It is worse than I thought, at the 1 minute mark, primary is drawing 7A while the slave is drawing 1A.

One has to wonder about why all the jumpy camera work. What are they trying to hide? It isn't that difficult to hold a camera steady, even zoomed in like the video in this post. If I can do it, why can't they instead of producing some vertigo inducing camera work? I will follow along your journey on this one, it might be quite entertaining.
 
Wait how does the 120v loading share on each unit, I thought each carried one leg and the compare the voltage angle to provide 240.

So if you apply a 1500-3000w single phase load on unit, the other is idle, are we saying the battery voltage at one inverter terminal will differ from the other so much they will shut down unless the impedance of each DC connection is absolutely identical?

IMO these set up’s will never have balanced loads between legs each inverter will have different loads and slightly different voltage drops on the leads from the battery.

Or is this whole shut down thing only apply to 240v loads and units sharing properly?
 
Wait how does the 120v loading share on each unit, I thought each carried one leg and the compare the voltage angle to provide 240.

So if you apply a 1500-3000w single phase load on unit, the other is idle, are we saying the battery voltage at one inverter terminal will differ from the other so much they will shut down unless the impedance of each DC connection is absolutely identical?

IMO these set up’s will never have balanced loads between legs each inverter will have different loads and slightly different voltage drops on the leads from the battery.

Or is this whole shut down thing only apply to 240v loads and units sharing properly?
I won't address your questions as I'm on my way out the door but this is Euro 230V, not US/North America 240V split phase.

Inverters are in parallel.
 
Does that negate what I just said? We'll see what the result is when it's all set up later this week. I prefer talking about facts, actual figures, not vague 'You might have problems' and the like. Still waiting for timselectric to tell us what size cables he had a problem with on his set up. I wonder why he isn't telling us.

It's best not to attack Tim's. He delves in the negative side of voltage voodoo.

Also, be aware that your particular inverters are of extremely low quality. They're going to be sensitive to any little thing that comes up.
 
One thing Tim is right about, these are 230V Euro inverters in parallel and one inverter will probably carry more load due to any slight difference in supply voltage.
A few observations.

* The lynx busbar in the system is a common voltage and current point. Differences in current between the busbar and the inverters does not create an imbalance at the battery.... Consequently the question raised by the OP does not involve balance of charge/discharge to the battery.
* A good inverter will coordinate with it's parallel partner to coordinate and balance so they are both driving the same amount of load. (Not all inverters do this)
* Without such coordination, slight variances on the AC wiring can cause noticeable differences in the balance on the AC between the two inverters.
When there are examples of inverters not driving equally, it would be interesting to find out if it is due to differences on the DC side or AC side.
* An inverter will draw the current it needs from the DC to drive what it thinks it needs on the AC side. If the voltage on the DC side is lower, it will draw more current. I guess anything is possible, but It is hard to imagine the DC voltage driving the AC out wattage unless the design of the inverter is really bad. (Note that the inverter has to drive the AC output to the correct voltage and current when the battery is fully charged. (59V) and when the battery is nearly fully discharged (48V) )
* The Victron guide talks about balancing the DC side because the inverter with lower voltage will draw more current, not because it will cause an imbalance in the output. The Victron guide points out that if the difference is large enough one inverter could fault out and ALL of the load would be on the other inverter. (I do not know, but I would bet the Victron inverters coordinate to ensure the inverters are driving equally.)
* If all the lugs, torque, connectors, fuses are identical, the only difference between the two sets of connections in the OPs picture appears to be about about 4 feet of 70mm^2 or 2/0 AWG wire. At 110A this is less than .1V of drop. (The chances are very good that differences in crimps, fuses and connections will cause a larger variance in the DC voltage seen by the inverters than the 4' of wire would)

Even though it is not the popular narrative on this thread, I still don't see an issue with the wiring shown in post #1. The one 'problem' is that if the inverters are running full out, when the batteries get really low the one with the 4' more of wire will kick of slightly before the other one. However, if it got to that, it would not happen very much sooner than if the DC was perfectly balanced. Other than that, I can not come up with an engineering explanation of why it would matter. I have been wrong before and I may be wrong about this, but I don't see it.
 
Given that the cables appear twice as long, twice as much as the other.



FIRST you argue with a career electrician...

THEN you demonstrate you have no clue how to use a tool and post a result nearly two orders of magnitude wrong.
Haaaa… ya see …. ya see…
but I will admit it’s fun to watch….
J.
 
* A good inverter will coordinate with it's parallel partner to coordinate and balance so they are both driving the same amount of load. (Not all inverters do this)

I'm not aware of any that do.

Victron != good inverter :p

* The Victron guide talks about balancing the DC side because the inverter with lower voltage will draw more current, not because it will cause an imbalance in the output. The Victron guide points out that if the difference is large enough one inverter could fault out and ALL of the load would be on the other inverter. (I do not know, but I would bet the Victron inverters coordinate to ensure the inverters are driving equally.)

Nope. They do not. They rely on a proper installation with equal resistance conductors of an appropriate size. They're pretty explicit about the importance in the reference.
 
Nope. They do not.

Victron Wiring Unlimited. Section 4.9.
"Different voltages mean different currents. The unit with a lower voltage
will have a higher current running through its power electronics. Inverter/
charger overload is triggered by the amount of this current. So, although the
power that each inverter delivers will be the same, the unit with the lower
voltage will have a larger current running through it and will go into overload
before the other units do. The total inverter power of the system will now
be less because when one unit goes into overload, the whole system will
stop working. The unit with bad wiring will determine the performance of the
whole system"
It is all a matter of degree. Everyone would agree that if one inverter had 100 ft more cable than the other it could be a problem.
I think everyone would agree that if one inverter had 1/16 inch more cable it would not matter. I simply assert that the 4' we are talking about does not make enough difference to worry about.
 
Victron Wiring Unlimited. Section 4.9.
"Different voltages mean different currents. The unit with a lower voltage
will have a higher current running through its power electronics. Inverter/
charger overload is triggered by the amount of this current. So, although the
power that each inverter delivers will be the same, the unit with the lower
voltage will have a larger current running through it and will go into overload
before the other units do. The total inverter power of the system will now
be less because when one unit goes into overload, the whole system will
stop working. The unit with bad wiring will determine the performance of the
whole system"
It is all a matter of degree. Everyone would agree that if one inverter had 100 ft more cable than the other it could be a problem.
I think everyone would agree that if one inverter had 1/16 inch more cable it would not matter. I simply assert that the 4' we are talking about does not make enough difference to worry about.

Unfortunately, we're pulling in adjacent issues through general statements. I responded to your claim that they coordinate. They do not.

See 6.9 (DOH! 6.7)

This is the reason I posted the last line in post #20: https://diysolarforum.com/threads/battery-cable-length-from-lynx-distributor.76642/#post-977966

Will it matter? It depends. @Zwy pointed out that this type of inverter in parallel may experience a fault simply based on the deviation in voltage measurements. That may also include any potential deviations purely from inaccuracy. Lord knows 0.1V deviation between two pieces of equipment measuring the same 50-ish volts is pretty common.

It's early in the installation and easy to fix. Given the amount of man-hours invested in the discussion, I would say the cost of two new cables of equal length would be at least a few of orders of magnitude lower than the value of life lost by those involved. :)
 