I have a bias for setting protection limits to actual limits. 2.5V low and 3.65V high. No damage occurs to cells operating in this range, so there's no reason to force the BMS to narrow this range.
Of course that requires you set the total voltage protection limits to 16X these values.
Set the recovery values to something sensible.
If these are the defaults established by the manufacturer, change at your own hazard.
You program the equipment to operate inside this range.
Cell diff pressure protection of 1V seems pretty extreme given that the cells have a 0.3V primary operating range (3.1-3.4V). I would adjust this to 0.5V