No check the whole home wiring backup diagrams in the manualOur main panel is 200amp main, so I don't need to split out critical loads to sub-panel from the load circuit of 18kpv?
The whole home backup diagram makes no sense...why would I have to install a manual transfer switch in the event that power goes out? So I'd have to walk out to garage and flip the switch? I would think that this would be automatic in the event of a power outage? Or am I just being a total newbie here? Help?No check the whole home wiring backup diagrams in the manual
The manual transfer is only used in rare cases of issues with the inverter, it's only used if the inverter has issues and it's own internal bypass isn't working, to restore power to the house by bypassing the inverter. During normal operations the inverter takes care of everything and automatically use power from grid, solar and battery as need. The manual transfer switch is optional.The whole home backup diagram makes no sense...why would I have to install a manual transfer switch in the event that power goes out? So I'd have to walk out to garage and flip the switch? I would think that this would be automatic in the event of a power outage? Or am I just being a total newbie here? Help?
So I don't need to connect anything to the load side of the inverter? Simply do the supply side taps to the "grid" terminals on the 18kpv and thats it?The manual transfer is only used in rare cases of issues with the inverter, it's only used if the inverter has issues and it's own internal bypass isn't working, to restore power to the house by bypassing the inverter. During normal operations the inverter takes care of everything and automatically use power from grid, solar and battery as need. The manual transfer switch is optional.
Your main panel goes on the load side of the inverter, and the grid side of the inverter goes to the meter, with a service disconnect switch between. All power passes thru the inverterSo I don't need to connect anything to the load side of the inverter? Simply do the supply side taps to the "grid" terminals on the 18kpv and thats it?
Just a heads up.Hopefully this isn't a redundant post. But looking for opinions, experience, and or suggestions before I pull the trigger on this system from Signature Solar.
So the design is EG4 18kPV All-In-One Hybrid Inverter, 24@ 400 watt Canadian Solar panels for 9.6kW (trying to stay under the 10kW Duke Energy requirements for the 1m liability policy), ground mount system utilizing IronRidge with anchor screws. Solar array will be approximately 120' from my garage where panel is located, so will trench the DC (10g) runs 3x8 to DC disconnects near meter then connected to inverter inside garage.
My questions:
1: I will most likely expand this system later. Addition of batteries, another array etc. What are thoughts about equipment, design with this in mind.
2: I am completely out of slots for the inverter to connect to my electrical panel, should I hire an electrical contractor to upgrade first? (currently have 200amp panel)
3: Permitting....has anyone pulled DIY/homeowner permits in Pasco County FL that has experience with the local gov?
4: Would you do anything different than my current plan?
Appreciate any thoughts and welcome your input/experience. Trying to get this ordered while free shipping during this month, and tax advantages before the end of the year.
If the arrays are identical, facing the same direction, and have no shading.. you can combine them on mppt #1. it'll clip off 1a of power during the absolute maximum production, which realistically you'll rarely see in the real world.Need advice please: EG4 18KPV has 3 MPPT inputs. Input #1 is system defined parallel. I currently have installed 2 strings of Canadian Solar CS6R-400MS-HL 400 watt panels in 12 panels per string. So my math is 12.99A at 441.6V (36.8 x 12). If I put both strings into MPPT #1 that will put the strings in parallel at 25.98A (which the inverter automatically limits the parallel connection to 25A).
So should I put one string in to MPPT #1 and second string into MPPT #2? In the very near future I will be adding another 12 panel of same brand and size. MPPT #2 and #3 are limited to 15A each.
View attachment 185264 View attachment 185266
Thank you, appreciate the help. Wasn't sure if running them on MPPT #1 in parallel made any significant difference. All panels facing same direction and no shading.If the arrays are identical, facing the same direction, and have no shading.. you can combine them on mppt #1. it'll clip off 1a of power during the absolute maximum production, which realistically you'll rarely see in the real world.
That said, the 18kpv has 3 MPPT's. you mention these 2 arrays and another 1 coming in the future. If that is the extent of your expansions, you could just do 1 string per MPPT. If you do that, you don't have to worry about the MPPT clipping the output at peak, and always have the option of combining those 2 strings into mppt1 later, should you decide to add another array in the future.
Real word though, I don't think either choice is "better" over the other. Just leave a bit of excess wire so you can move the arrays around later if needed.
Thank you, appreciate the help. Wasn't sure if running them on MPPT #1 in parallel made any significant difference. All panels facing same direction and no shading.