Yes, the cc is set to -30mv/degree C.
Settings from Kilovault state 28.4 bulk/absorb for 24v.
Can you explain how you come to 14.85/ 29.7?
Not sure if you have resolved this issue or not. Just found your thread. I have the same batteries and they are close to dead after 18 months. There is a typo in the installation and user manual for the temperature compensation variable. Section 4.1.2 shows the value as you state above: -30mv/degree C.
However, at the end of 4.2.4, it is listed as -3mV/°C
Further, in the integration guide here:
https://kilovault.com/wp-content/up...W_Pro_KiloVault_Integration_Guide_May2021.pdf
the value is listed as -3mV/°C at the bottom of advanced settings for the PLC 2100 section.
-3mV/°C appears to be the correct value.
The PLC 2100 was a new product rolled out in March 2020. Kilovault is still figuring it out.
I damaged my batteries by overcharging for several weeks until someone finally found (or wrote) the integration guide and sent it to me. The temperature compensation was the problem. When I entered the correct value, charging appeared to be normal.
Now with the batteries at around 50 deg F., I'm getting almost nothing out of them when charging is removed. With a charge session in the evening just before I go to bed, they cannot maintain above 50% with a mere 5 amp AC load. Pathetic.
Waiting on a response to my warranty claim.