Hello everyone. A quick introduction. I'm a 42 years old with 4 kiddos and a wife. Each year my family sets out on a 40-50 day road trip with our fifth wheel. I also use the fifth wheel for hunting trips, bike race trips, boondocking in Moab, etc. This year we changed out of our big toy hauler that had a massive onboard generator and I'd like to make my life a little easier, thus I'm venturing into the inverter world along with solar.
Attached is a very garbage diagram I made. (I have never and will never be good at putting visuals on paper)
Goals:
Comfortably run one 15 BTU AC on a Honda EU2000i, 1600W/13.3A Continuous, while adding some small headroom for short Microwave runs, along with some other very low draw items like lights, tvs, starlink, water pump, furnace fan. Obviously we would not be running all of these at the same time. I have a 2nd EU2000i that I can connect in parallel for 3200W/26.6A continuous, if I should intend on firing up a 2nd AC or using coffee pots, Blackstone or other high draw appliances.
Plan:
Quattro II 24V 3000W that will provide extra supply when needed while on generators, and can also run one AC temporarily when we stop to make lunch at rest areas or museums where we could spend an hour while the dogs hang out in the fiver. (I did wire in a front plug for the generators so I can quickly connect the fiver to the generator in the back of my truck should the AC be too much to run off of battery for a bit)
Equipment:
Quattro II 3000W 24V 120 -
I picked this model because of the built in transfer switch for shore/generator power, this helps me keep things neat and tidy.
Orion 24-12V 70A Step down - Break away switch, some lights up front, and the electric front leveling jacks are all currently directly wired to the 12v battery and I'd wire these to a bus bar that is fed by the Orion. There is also a 6 AWG wire running from the 12V battery to the convertor, I believe I could technically disconnect this but then if we turn off the inverter, we would not have 12v, so I plan on connecting that to the "12v bus bar" as well.
Victron MPPT 30AMP -
This would be for my first 1000 Watts of solar. I would add a second one should I add more panels later.
BMV 712 w/ shunt
I've had this for years, it has the display thing on it, but I usually just roll it up in the compartment and connect with Bluetooth.
Cerbo GX
I think this is going to be very essential for me, I'd love to turn on DVCC, but it's also possible I have no idea what I'm talking about. Either way, this would be very nice to have so I can easily change settings on the Quattro without breaking out the laptop. For instance, setting the input voltage to around 13 Amps when on generator power so that the Quattro can help out.
I'm sure my diagram is going to suck to read so I'll type it out as well for those willing to read.
1. The quattro's AC Out 1 will be connected directly to my distribution panel, making the entire camper able to be powered by the inverter. (I know it can't power everything at once)
2. The DC Positive will come out of the Quattro and have a battery disconnect, then a 300AMP fuse right before the positive connection to a 24V 200amp hour bank made out of 2 24v 100 batteries in parallel.
3. I would then run what I believe would be a 6 AWG wire from the positive battery terminal to a 24V Bus Bar. This bus bar will power the origion 24-12V and cerbo GX, The 24V bus bar will also be fed by the MPPT. The shunt will have it's positive wire connected here as well.
4. The 24-12v step down will have a bus bar, one 6 AWG wire going to the fiver's converter, the other going to a bus bar to feed the electric leveling jacks, break away, and some lights that are currently directly wired to the 12V battery.
5. The shunt will come off the negative side of the battery and be connected to the negative bus bar along with the Quattro, step down, MPPT, and cerbo
6. Diagram doesn't show it, but I'd also add a battery disconnect between the positive battery terminal and the 24V Bus Bar.
My questions outside of whatever advice you will all give me..
1. Do I need a fuse close to the Orion 24-12v converter feed line? I don't believe the existing line shows one today, but was wondering if it's a good idea. My biggest fuse in the converter is currently 30AMP for slide, and I really don't see us using more than 70AMP at a time on the DC side. Would a fuse be warranted here? Size?
2. My wire sizes could and most likely are, not correct as I have not sized those yet, due to wanting to run this setup by everyone first.
3. Solar Circuit Breaker Sizing - 40AMP?
4. Should I move the 24-12V Orion to the 24V Bus Bar or is it ok to leave on positive terminal? As I type this I realize I'd probably need an additional battery disconnect unless I move it to the 24V bus bar...
5. Am I missing essential fuses or sized wrong on what's on the diagram? 300 on main line, 10 on cerbo GX positive, 40amp Breaker before MPPT. ...Do I need something between MPPT and 24V bus bar?
6. My local victron rep recommended I add 2 multiplus devices instead of the Quattro, this is out of my budget but he has me worried about what to do if the Quattro somehow fails on me. I was considering some type of bypass but it just feels unsafe to me and would like to see if there are recommendations on a way to safely bypass the Quattro with shore power so we can at least get back to ongrid living if the Quattro should fail.
7. The victron rep also recommended a small lithium 12v battery attached between the 24-12v Orion and my 12v bus bar. I assume he would have then had me tune the Orion to around 13.2 volts or so to keep that battery up, but I don't believe that's what the Orion is for and I'm not exactly sure why I would need the buffer battery since 30AMPs is my biggest slide and I'd assume the 70AMP Orion can handle that fine?
If anyone actually reads all this and calls me out on stupid stuff, I appreciate you and thank you :-D
Attached is a very garbage diagram I made. (I have never and will never be good at putting visuals on paper)
Goals:
Comfortably run one 15 BTU AC on a Honda EU2000i, 1600W/13.3A Continuous, while adding some small headroom for short Microwave runs, along with some other very low draw items like lights, tvs, starlink, water pump, furnace fan. Obviously we would not be running all of these at the same time. I have a 2nd EU2000i that I can connect in parallel for 3200W/26.6A continuous, if I should intend on firing up a 2nd AC or using coffee pots, Blackstone or other high draw appliances.
Plan:
Quattro II 24V 3000W that will provide extra supply when needed while on generators, and can also run one AC temporarily when we stop to make lunch at rest areas or museums where we could spend an hour while the dogs hang out in the fiver. (I did wire in a front plug for the generators so I can quickly connect the fiver to the generator in the back of my truck should the AC be too much to run off of battery for a bit)
Equipment:
Quattro II 3000W 24V 120 -
I picked this model because of the built in transfer switch for shore/generator power, this helps me keep things neat and tidy.
Orion 24-12V 70A Step down - Break away switch, some lights up front, and the electric front leveling jacks are all currently directly wired to the 12v battery and I'd wire these to a bus bar that is fed by the Orion. There is also a 6 AWG wire running from the 12V battery to the convertor, I believe I could technically disconnect this but then if we turn off the inverter, we would not have 12v, so I plan on connecting that to the "12v bus bar" as well.
Victron MPPT 30AMP -
This would be for my first 1000 Watts of solar. I would add a second one should I add more panels later.
BMV 712 w/ shunt
I've had this for years, it has the display thing on it, but I usually just roll it up in the compartment and connect with Bluetooth.
Cerbo GX
I think this is going to be very essential for me, I'd love to turn on DVCC, but it's also possible I have no idea what I'm talking about. Either way, this would be very nice to have so I can easily change settings on the Quattro without breaking out the laptop. For instance, setting the input voltage to around 13 Amps when on generator power so that the Quattro can help out.
I'm sure my diagram is going to suck to read so I'll type it out as well for those willing to read.
1. The quattro's AC Out 1 will be connected directly to my distribution panel, making the entire camper able to be powered by the inverter. (I know it can't power everything at once)
2. The DC Positive will come out of the Quattro and have a battery disconnect, then a 300AMP fuse right before the positive connection to a 24V 200amp hour bank made out of 2 24v 100 batteries in parallel.
3. I would then run what I believe would be a 6 AWG wire from the positive battery terminal to a 24V Bus Bar. This bus bar will power the origion 24-12V and cerbo GX, The 24V bus bar will also be fed by the MPPT. The shunt will have it's positive wire connected here as well.
4. The 24-12v step down will have a bus bar, one 6 AWG wire going to the fiver's converter, the other going to a bus bar to feed the electric leveling jacks, break away, and some lights that are currently directly wired to the 12V battery.
5. The shunt will come off the negative side of the battery and be connected to the negative bus bar along with the Quattro, step down, MPPT, and cerbo
6. Diagram doesn't show it, but I'd also add a battery disconnect between the positive battery terminal and the 24V Bus Bar.
My questions outside of whatever advice you will all give me..
1. Do I need a fuse close to the Orion 24-12v converter feed line? I don't believe the existing line shows one today, but was wondering if it's a good idea. My biggest fuse in the converter is currently 30AMP for slide, and I really don't see us using more than 70AMP at a time on the DC side. Would a fuse be warranted here? Size?
2. My wire sizes could and most likely are, not correct as I have not sized those yet, due to wanting to run this setup by everyone first.
3. Solar Circuit Breaker Sizing - 40AMP?
4. Should I move the 24-12V Orion to the 24V Bus Bar or is it ok to leave on positive terminal? As I type this I realize I'd probably need an additional battery disconnect unless I move it to the 24V bus bar...
5. Am I missing essential fuses or sized wrong on what's on the diagram? 300 on main line, 10 on cerbo GX positive, 40amp Breaker before MPPT. ...Do I need something between MPPT and 24V bus bar?
6. My local victron rep recommended I add 2 multiplus devices instead of the Quattro, this is out of my budget but he has me worried about what to do if the Quattro somehow fails on me. I was considering some type of bypass but it just feels unsafe to me and would like to see if there are recommendations on a way to safely bypass the Quattro with shore power so we can at least get back to ongrid living if the Quattro should fail.
7. The victron rep also recommended a small lithium 12v battery attached between the 24-12v Orion and my 12v bus bar. I assume he would have then had me tune the Orion to around 13.2 volts or so to keep that battery up, but I don't believe that's what the Orion is for and I'm not exactly sure why I would need the buffer battery since 30AMPs is my biggest slide and I'd assume the 70AMP Orion can handle that fine?
If anyone actually reads all this and calls me out on stupid stuff, I appreciate you and thank you :-D