Awesome. I assumed I should have the PV disconnect, and rsd installed also. Is there any chance for export in this scenario? Do I even need to alert my power company?
With an 18kpv, there will likely be some export regardless of your settings. When a large load suddenly cuts off, the power has to go somewhere.
With 6000xp, not likely. The 6000xp is either on-grid (powering load and charging battery), or off-grid supplying load. The inverter does not seem to be ever connected to the grid, except to charge batteries (which is taking power, not pushing power).
Not correct.
In off-grid mode, it disconnects from the grid via relays but does still monitor the grid so that it stays synced.
If it needs the grid due to overload, it will close the relays and go into grid assist/bypass mode.