Currently have 16 rec n peak 330 watt panels wired 4 in seires going to a combiner box 100 ft from array at the power room.
Current charge controler can handle the hogher AMPs but am considering going to 2 EG4 6000xp all in one inverters in parallel.
Question is how to wire the 4 strings of panels to the 6000xp.
Is it possible to series the panels together at the combiner box location 100 feet from the panels? Making 8 in series.
The Eg4 6000xp specs
Startup V 100
Input range 100 - 480 V
MPP operating range 100 - 385 V
Nominal MPP V 320.
Any thoughts on best option? Thanks!
Current charge controler can handle the hogher AMPs but am considering going to 2 EG4 6000xp all in one inverters in parallel.
Question is how to wire the 4 strings of panels to the 6000xp.
- Vmp: 34.6 Volts
- Voc: 41.0 Volts
- Imp: 9.55 Amps
- Isc: 10.33 Amps
Is it possible to series the panels together at the combiner box location 100 feet from the panels? Making 8 in series.
The Eg4 6000xp specs
Startup V 100
Input range 100 - 480 V
MPP operating range 100 - 385 V
Nominal MPP V 320.
Any thoughts on best option? Thanks!