Hamish
New Member
No joy. Does it have to be 65v or just anything >64v?Just curious, did you get a chance to set it at 65v? Did it start operating as you'd hoped?
No joy. Does it have to be 65v or just anything >64v?Just curious, did you get a chance to set it at 65v? Did it start operating as you'd hoped?
I tried setting CSV>64 but the system is still selling power from the batteries. Same result as the last time I tried this. ??
Anyhow, thanks very much for that document. I have over 90 documents but I didn't have that one. It is very informative.
I am not sure where to go from here. In a previous blog someone mentioned that sometimes the xw gets stuck in off grid mode. I fixed that once by doing a complete power down of the system and then Rebooted when I brought it back up. I think I will try that this morning along with the gsv=66 trick.
@Hamish Is this a typo? It needs to be 65. 65 and higher enables enhanced grid support.tried setting CSV>64
No joy. Does it have to be 65v or just anything >64v?
Interesting. I did exactly the same thing. I also added an exhaust fan in the ceiling, but that's another story. I think one of the reasons my previous XP failed was that the fans failed. Schneider does not like to invest in decent fans, and my neighbor also had one of the fans fail. So I basically don't trust the fans in these units, and augment them with additional fans. Of course, Schneider does not provide a source for parts, so if one of your fans does go, you have to do a lot of research to find a replacement. He found one somewhere in Denmark.No, my XW will not support closed loop with the Trophy batteries. The older, original XW's were not designed to be controlled externally (except from the SCP), as far as I know.
I've got to say that the XW has been bulletproof so far. Once I commissioned the system in 2011, it was not turned off until I did the expansion of the system earlier this year. Now I have 10.4kw of solar, with one array facing SE, one SW, and the newest facing directly south. My PV production curve during the day is fairly flat, with the XW showing a bit better than 6kw selling back to grid for a good part of the day, with almost 8kw total solar production at times. I have gotten 50+ kwh's/day during several days this summer. Yesterday, I got 36kwh's (I have too many trees blocking the low winter sun angle).
I did add a couple of fans to my system to help alleviate the heat buildup. Everything is mounted inside my house in a separate mechanical room, which also houses my solar water heaters and geothermal unit. It can get up to about 85 degrees in there even with the air conditioner on. I put a double computer type fan on top of the inverter, pulling air up through the unit, and a 9" diameter circular fan blowing across the SCC's. This made a BIG difference on the operating temps of the units. I don't see any temperature derating at all.
Not a typo: >64 means greater than 64. I.e. 65, 66, ...@Hamish Is this a typo? It needs to be 65. 65 and higher enables enhanced grid support.
If it's a typo, and you actually used 65.. something is off in your setup. Enhanced grid support would not be selling battery power to grid, under any scenario I am aware of. If it's not a typo, update it to 65 (as mentioned in several of my posts and the linked document) and see if the behavior changes.
It would be really nice, though not expected, if the Insight home had a way to report State transitions. As in when & why did it go into absorb mode. A plot of these state changes would be really, really nice. Helpful even.@Hamish Is this a typo? It needs to be 65. 65 and higher enables enhanced grid support.
If it's a typo, and you actually used 65.. something is off in your setup. Enhanced grid support would not be selling battery power to grid, under any scenario I am aware of. If it's not a typo, update it to 65 (as mentioned in several of my posts and the linked document) and see if the behavior changes.
I'd hold off until you change GSV to 65.Not a typo: >64 means greater than 64. I.e. 65, 66, ...
I think something is off it the setup/firmware. I am in the process of doing a complete power down, waiting for the Caps to discharge, and when I bring it back up I will reload the firmware, do a factory boot and rebuild all the settings. This has been a major pain in the rear since the first of June.
Just setting the GSV to 65 didn't do it. Then what I did was a complete grid power down, MPPTs, including batteries, came up batteries first MPPT second and grid last. Then I reset the inverter to factory. Then I went in and made sure all the settings were as before including setting GSV to 65. While doing this I noticed the battery type had been reset to custom. Previously it was Li-Ion. I left it at "custom" and went into where they hide the battery type: Top > Setup > Left menu > BMS Setup > Discover 6055. I left that as is, and went into the XW, > config, > Advanced, > battery settings, > battery type and left it at custom. I don't know if it was the Hocus Pocus with the batteries or the complete reset which solved the problem, assuming it is solved. For now it is working as it should and I will let it cook overnight and check it again in the morning.I'd hold off until you change GSV to 65.
Once you've done that, if you still see it acting up, then do the factory reset. but, until GSV is set to 65v, it won't behave in "enhanced grid support" mode.
Just setting the GSV to 65 didn't do it. Then what I did was a complete grid power down, MPPTs, including batteries, came up batteries first MPPT second and grid last. Then I reset the inverter to factory. Then I went in and made sure all the settings were as before including setting GSV to 65. While doing this I noticed the battery type had been reset to custom. Previously it was Li-Ion. I left it at "custom" and went into where they hide the battery type: Top > Setup > Left menu > BMS Setup > Discover 6055. I left that as is, and went into the XW, > config, > Advanced, > battery settings, > battery type and left it at custom. I don't know if it was the Hocus Pocus with the batteries or the complete reset which solved the problem, assuming it is solved. For now it is working as it should and I will let it cook overnight and check it again in the morning.
Just setting the GSV to 65 didn't do it. Then what I did was a complete grid power down, MPPTs, including batteries, came up batteries first MPPT second and grid last. Then I reset the inverter to factory. Then I went in and made sure all the settings were as before including setting GSV to 65. While doing this I noticed the battery type had been reset to custom. Previously it was Li-Ion. I left it at "custom" and went into where they hide the battery type: Top > Setup > Left menu > BMS Setup > Discover 6055. I left that as is, and went into the XW, > config, > Advanced, > battery settings, > battery type and left it at custom. I don't know if it was the Hocus Pocus with the batteries or the complete reset which solved the problem, assuming it is solved. For now it is working as it should and I will let it cook overnight and check it again in the morning.
Not so fast. I did all that and set GSV to 65. Overnight it stopped working. That is to say, the batteries were drawn down to 3%. Nothing seemed correct. I have done the power down, reload firmware, reboot, power up, power down blah blah blah. At this point the cc's shut down after almost exactly 2:15 minutes. Independently of that, the inverter either goes to the "000" or "---" state. I have checked all the settings Thrice, and I had my IT department check them as well. I have about had it with this POS. Three months ago, I was about || this close to having it ripped out and replacing it with Outback equipment. I am almost there again. If this was a car, I would invoke the Lemon Law.This is great to hear!
Not so fast. I did all that and set GSV to 65. Overnight it stopped working. That is to say, the batteries were drawn down to 3%. Nothing seemed correct. I have done the power down, reload firmware, reboot, power up, power down blah blah blah. At this point the cc's shut down after almost exactly 2:15 minutes. Independently of that, the inverter either goes to the "000" or "---" state. I have checked all the settings Thrice, and I had my IT department check them as well. I have about had it with this POS. Three months ago, I was about || this close to having it ripped out and replacing it with Outback equipment. I am almost there again. If this was a car, I would invoke the Lemon Law.
I will try to calm down and try again, wasting yet another day.
Thanks again for the App Note link you sent. I missed (forgot? one little thing causing problems getting it into Enhanced Grid Support.@Hamish something you said didn't make sense to me, was that the BMS was setting your recharge SOC to "98%" when you wanted it at 100%. It kept bugging me, so this morning I went through and re-read your post. In re-reading it, I see i missed a fundamental part. You wanted your recharge SOC at 100%.
I suspect it's not the BMS resetting your recharge SOC to 98%, but the XW firmware itself. If you set recharge SOC to 100%, this would mean to *always* have your batteries recharging. which is likely not good for your batteries. Thus, I suspect it's an undocumented "self preservation, so you don't shoot yourself in the foot" feature in the firmware itself. I did look through the XW documentation to see if there was any mention of it, but I didn't see any. But fundamentally "recharge SOC 100%" just doesn't make any sense in any use-case I can think of. In fact, taking this a step further.. "recharge soc 100%" would be functionally equivalent to a float charge. in which case, you'd enable 3stage charging, not 2 stage. (I'd advise against it since you want to sell to the grid). but honestly, I think this boils down to you wanting to do something with your inverter, that you probably *shouldn't* do.
I mentioned this in post 38I missed (forgot? one little thing causing problems getting it into Enhanced Grid Support.
Still no joy.Just setting the GSV to 65 didn't do it. Then what I did was a complete grid power down, MPPTs, including batteries, came up batteries first MPPT second and grid last. Then I reset the inverter to factory. Then I went in and made sure all the settings were as before including setting GSV to 65. While doing this I noticed the battery type had been reset to custom. Previously it was Li-Ion. I left it at "custom" and went into where they hide the battery type: Top > Setup > Left menu > BMS Setup > Discover 6055. I left that as is, and went into the XW, > config, > Advanced, > battery settings, > battery type and left it at custom. I don't know if it was the Hocus Pocus with the batteries or the complete reset which solved the problem, assuming it is solved. For now it is working as it should and I will let it cook overnight and check it again in the morning.
Why are you concerned about a 2% hysteresis? That's actually very reasonable. As far as I know even in enhanced mode the charge controllers are not a PID type, they need some kind of "dead band". Just like a thermostat on an HVAC system, it cannot keep the room temp at an exact value. It swings a little both ways.