So, I found this on the IAEI (International Association of Electrical Inspectors) website...
ON THE GROUNDING AND BONDING OF SOLAR PHOTOVOLTAIC SYSTEMS
Fundamentals of Grounding and Bonding
By Joseph A. Kraft / Published in January/February 2021
News & Research / IAEI Magazine / 2021 /
2021 January/February / Features
Fundamentals of Grounding and Bonding
By Joseph A. Kraft / Published in January/February 2021 Share |
PV Systems
The Array
A decade ago, it was common practice to bond the metal frames of PV modules by drilling and tapping a hole in the aluminum frame of each module, fastening a lay-in lug to each, and then connecting those lugs with a bare, stranded, copper conductor. Connectors that were made of incorrect materials were sometimes installed, which, owing to their relative position to copper in the galvanic series, would corrode and, eventually, fail. This violated the requirement in Section 110.14 that connectors be identified for the material of the conductor. Another problem was that the surfaces of module frames, being exposed to the elements, would, over time, develop a thin layer of aluminum oxide on their surfaces. This oxide layer was electrically insulative and compromised the conductive integrity of the module/lug connection. Lugs and wire can still be used for bonding PV modules, but the lugs are now required to be listed for the application, per 690.43(A).
In recent years, products have been developed to comply with the requirements of 690.43 by using the very frames upon which the PV modules are mounted to bond the modules. Many metallic PV racking systems are now listed to UL 2703 to support and bond PV modules. Modern practice requires only an equipment grounding conductor to be run from an array where the modules are so bonded. Where the equipment grounding conductor leaves the vicinity of the array, it is required to be run with the circuit conductors, per 690.43(C), and shall be sized per 250.122. If the equipment grounding conductor is smaller than No. 6 AWG, it is required to be protected from physical damage, per 250.120(C).
At one time, the prevailing wisdom required a grounding electrode conductor to be installed from the array to its own grounding electrode or to the premises grounding electrode system. If a separate grounding electrode system for the array was installed, it was required to be bonded to the premises grounding electrode system. While a separate grounding electrode system is still permitted to be installed for a PV array, per 690.47(B), it is no longer required to be bonded to the premises grounding electrode system.
----------------------------------------------------
To me it sounds as if they are saying that if a stand-alone earthing system (properly installed rods and wiring) is allowed and is not required to be connected back to the bonded grounding system at the main panel at the house. Or am I confused still?
Any thoughts?