In recent years, products have been developed to comply with the requirements of 690.43 by using the very frames upon which the PV modules are mounted to bond the modules. Many metallic PV racking systems are now listed to UL 2703 to support and bond PV modules. Modern practice requires only an equipment grounding conductor to be run from an array where the modules are so bonded. Where the equipment grounding conductor leaves the vicinity of the array, it is required to be run with the circuit conductors, per 690.43(C), and shall be sized per 250.122. If the equipment grounding conductor is smaller than No. 6 AWG, it is required to be protected from physical damage, per 250.120(C). At one time, the prevailing wisdom required a grounding electrode conductor to be installed from the array to its own grounding electrode or to the premises grounding electrode system. If a separate grounding electrode system for the array was installed, it was required to be bonded to the premises grounding electrode system. While a separate grounding electrode system is still permitted to be installed for a PV array, per 690.47(B), it is no longer required to be bonded to the premises grounding electrode system.
----------------------------------------------------
To me it sounds as if they are saying that if a stand-alone earthing system (properly installed rods and wiring) is allowed and is not required to be connected back to the bonded grounding system at the main panel at the house. Or am I confused still?
Any thoughts?
I worked with a data center that had double-ended substations all over the facility, each side had a dedicated neutral-ground bond. The data center was from the "ground the hell out of it" era. One vendor complained about signal noise on the ground, so we started investigating. You could measure 200A on a raised floor stringer. (Negligible voltage, but negligible ground resistance due to system design.)I'd love to see some references for ground loop issue in power wiring (even if it's just EMI/RFI), since I have a really thin bibliography for it.
If you connect the EGC of the array to the array's ground rod, then it is not an effective ground fault path for either AC fault onto DC conductors (yes, it's possible) nor for DC side ground faults (some DC ground fault detection systems check for a DC current path through the EGC)
I didn't read anything about something they "didn't recommend" or "wasn't required".
It stated that it is still permitted...as in it was permitted before.
And I didn't see a single word "backbonded". And it pretty clearly states..." it is no longer required to be bonded to the premises grounding electrode system."
"While a separate grounding electrode system is still permitted to be installed for a PV array, per 690.47(B), it is no longer required to be bonded to the premises grounding electrode system."
Read this post again: https://diysolarforum.com/threads/what-is-the-simple-answer-for-off-grid-grounding.70317/post-890173I asked Victron about AC being introduced into the DC side of the system. Here is their response...
"Quattro provides galvanic isolation between AC and DC."
So if I am hearing them correctly there would be no AC current backfeeding into the array's DC wiring. Do you read it the same way? You have me concerned and would like to hear your opinion on what this actually means.
Thank you in advance.
Lightning protection system has to be bonded to ground system as well:Tangential conversation. I plan on adding some lightning protection to my ground mounts by installing a line of connected lighting rods on poles every 20-25 feet roughly 20 ft in front of the mounts. Same concept as the peak roof line of a building. Plus l have MidNite SPDs on all incoming circuits (AC and DC).
My arrays are 280 feet away and no way am I gonna send that current to my power shed. And it won’t be attached to shit other than poles. The mounts and panels won’t be connected. Trying to keep any direct strikes from NOT going through them, but hit elsewhere.Lightning protection system has to be bonded to ground system as well:
250.106 Lightning Protection SystemsThe lightning protection system ground terminals shall be bonded to the building or structure grounding electrode system.Also see NFPA 780-2017, Standard for the Installation of Lightning Protection Systems, which contains detailed information on grounding, bonding, and side-flash distance from lightning protection systems.
I might even go with a single one of those ESE rods on a longer pole located a bit further away. If I can ascertain whether or not they are snake oil. And if I can buy or build one that’s not at oil field pricing.My arrays are 280 feet away and no way am I gonna send that current to my power shed. And it won’t be attached to shit other than poles. The mounts and panels won’t be connected. Trying to keep any direct strikes from NOT going through them, but hit elsewhere.
Just curious, I am still pretty new at this.Victron (Tier 1ish) vs white label Chinesium.
My arrays are 280 feet away and no way am I gonna send that current to my power shed. And it won’t be attached to shit other than poles. The mounts and panels won’t be connected. Trying to keep any direct strikes from NOT going through them, but hit elsewhere.
Victron is not the NEC. Only one requirement and quite simple.So here is what Victron had to say...
"Off-grid system grounding
Do not ground the positive or negative of the PV array. The PV negative
input of the MPPT is not isolated from the negative output. Grounding the
PV will therefore result in ground currents. The PV frames however may
be grounded, either close to the PV array or (preferably) to the central
ground."
So if I am reading this correctly...The PV frames can be grounded at the array itself...OR...it can be grounded back at the main panel house ground. And they are recommending it be done back at the house main panel grounding point.
The lightning knows that those wires are for PV only, so it doesn't use them.Just curious, I am still pretty new at this.
Without grounding, how do you keep the the extra energy from just using your conductors to go from panels to shed?
Lightning is so courteous these daysThe lightning knows that those wires are for PV only, so it doesn't use them.
I understand your thought process about this.My arrays are 280 feet away and no way am I gonna send that current to my power shed. And it won’t be attached to shit other than poles. The mounts and panels won’t be connected. Trying to keep any direct strikes from NOT going through them, but hit elsewhere.
Lighting protection and grounding are two different (separate) things.Just curious, I am still pretty new at this.
Without grounding, how do you keep the the extra energy from just using your conductors to go from panels to shed?
Sigh…reread what I said. The lighting protection will be completely separate from the bonded panels with the ground going back to the main. Two different things. The lighting protection won’t even be touching the mounts or panels. It’s job is to try to be a better target so any lighting strikes it rather than the panels.Just curious, I am still pretty new at this.
Without grounding, how do you keep the the extra energy from just using your conductors to go from panels to shed?