400bird
Solar Wizard
Right, my mistake. I think the other portion of my post is still valid. The XW doesn't have the capability to and never will bond ground to neutral.All the neutrals for AC1, AC2 & Load are hard wired together at the terminal block, that never changes. We are only talking about there potentially being a relay that makes or breaks a connection between N-G so unless there was a ground fault somewhere, your system would work normally with or without a N-G connection.