silverstone
Solar Enthusiast
- Joined
- May 3, 2022
- Messages
- 1,044
It seems to be a common issue. Yeah, at first I didn't think it was important. Duh .
I mean, the way to ensure that the batteries get fully charged is to keep a "reference voltage" for the inverter/charger of say 55V-56V for a 16s Pack (3.43VDC/cell - 3.50VDC/cell although at 56V I will hit OVP on one of the cells if I do it "open-loop", i.e. without feedback and lowering the voltage when I get "close" to say 3.55VDC).
So typically at the end of the day, that's what I do (open-loop only, so the "tail current" can get quite low at 55VDC reference voltage).
But I see quite wide variety between my 2 batteries. And the SoC reporting I believe it's quite inaccurate. If I trust the BMS readout, I'd say that my inverters have a no-load (idle) loss of about 400W-600W (3 inverters x 3ph Deye 12kW/each Inverters in parallel in "off grid mode" only). That's 9.6kW-14.4kWh / day .
It can be simply because they were NOT top balanced in the beginning (JK BMS has an active balancer though), 1 cell is from a ~10 month old batch in the second battery, simply the SoC is determined by the lowest SoC cell which impacts a lot one battery and the voltage measurement "tolerance" are quite high (one BMS has approx 0.7V total pack voltage more than the other). Yep ... I do NOT think that's a body diode voltage drop though (VF).
So I'm debating whether I should install a "Smart Shunt" in my future batteries. Originally I was thinking about a DC Current Transducer, but these can have quite HIGH DC offset. Not an issue if you want to measure AC current but for DC measurement the DC offset can be critical, especially when using it for "coulomb counting" (SoC measurement based on integration of the current measurement over time).
I guess a Shunt + Precision Op-Amps Circuitry can get around that problem (DC offset) better.
So the question is: is it really worth to get the Victron Smartshunt (500 A is quite high ... I max out at 100 A long term, maybe 150 Apeak for OCP on the BMS), so I'm a bit disappointed that 500A is Victron's smallest Smart Shunt ? Or are there good Chinese clones ? I don't really need all the bells and whistles. And 200A shunt would be probably more than enough.
Preferred connection method would be RS232, RS485, Wifi/MQTT. BLE/Bluetooth I'm not too fond of (unless there is something easy to use like https://github.com/syssi/esphome-jk-bms) that I can then use to interface with MQTT etc. And some community "driver" or python script wrapper etc available would of course be a plus.
Thanks for your help
I mean, the way to ensure that the batteries get fully charged is to keep a "reference voltage" for the inverter/charger of say 55V-56V for a 16s Pack (3.43VDC/cell - 3.50VDC/cell although at 56V I will hit OVP on one of the cells if I do it "open-loop", i.e. without feedback and lowering the voltage when I get "close" to say 3.55VDC).
So typically at the end of the day, that's what I do (open-loop only, so the "tail current" can get quite low at 55VDC reference voltage).
But I see quite wide variety between my 2 batteries. And the SoC reporting I believe it's quite inaccurate. If I trust the BMS readout, I'd say that my inverters have a no-load (idle) loss of about 400W-600W (3 inverters x 3ph Deye 12kW/each Inverters in parallel in "off grid mode" only). That's 9.6kW-14.4kWh / day .
It can be simply because they were NOT top balanced in the beginning (JK BMS has an active balancer though), 1 cell is from a ~10 month old batch in the second battery, simply the SoC is determined by the lowest SoC cell which impacts a lot one battery and the voltage measurement "tolerance" are quite high (one BMS has approx 0.7V total pack voltage more than the other). Yep ... I do NOT think that's a body diode voltage drop though (VF).
So I'm debating whether I should install a "Smart Shunt" in my future batteries. Originally I was thinking about a DC Current Transducer, but these can have quite HIGH DC offset. Not an issue if you want to measure AC current but for DC measurement the DC offset can be critical, especially when using it for "coulomb counting" (SoC measurement based on integration of the current measurement over time).
I guess a Shunt + Precision Op-Amps Circuitry can get around that problem (DC offset) better.
So the question is: is it really worth to get the Victron Smartshunt (500 A is quite high ... I max out at 100 A long term, maybe 150 Apeak for OCP on the BMS), so I'm a bit disappointed that 500A is Victron's smallest Smart Shunt ? Or are there good Chinese clones ? I don't really need all the bells and whistles. And 200A shunt would be probably more than enough.
Preferred connection method would be RS232, RS485, Wifi/MQTT. BLE/Bluetooth I'm not too fond of (unless there is something easy to use like https://github.com/syssi/esphome-jk-bms) that I can then use to interface with MQTT etc. And some community "driver" or python script wrapper etc available would of course be a plus.
Thanks for your help