What would be the optimal setup for 30 Canadian Solar 400W Mono-crystalline Panels (CS6R-400MS-HL) feeding an 18KPV Inverter/Charger? I was thinking 3 strings of 10 panels each. Too simple? Am I missing something?
Panel Details:
Nominal Max. Power (Pmax) 400W
Opt. Operating Voltage (Vmp) 30.8 V
Opt. Operating Current (Imp) 12.99 A
Open Circuit Voltage (Voc) 36.8 V
Short Circuit Current (Isc) 13.85 A
Inverter Details:
Number of MPPTs 3
Inputs per MPPT 2/1/1
Max. Usable Input Current 25/15/15A
Max. Short Circuit Input Current 31/19/19A
DC Input Voltage Range 100–600 VDC
Unit Startup Voltage 100 VDC
Load Output Minimum Voltage >140 VDC
MPP Operating Voltage Range 120–500 VDC
Full Power MPPT Voltage Range 230–500 VDC
Nominal MPPT Voltage 360 VDC
Maximum Utilized Solar Power 18kW
Recommended Maximum Solar Input 21kW