  • Post in thread: Got a mess

    After rereading the post, it looks like it is 12V. A 1500W load at 12V would require inverter supply wire ampacity of 174A. That's calculated as 1500/12/inverter efficiency, so assuming 90%, 1500/12/.9 = 139A. NEC requires wire of 125% of that ampacity, so 139 * 1.25 = 174A. If a free air...
  • Post in thread: Checking My Numbers

    Happy to help out! Good luck with the project. Feel free to PM me if you have more questions.
  • Post in thread: Moving Inverter, 100' run Copper or Aluminum direct bury?

    Have you thought about 2-2-4 urd aluminum. Its around $2.60/ft. Don't bring it up into any building and seriously consider putting it in conduit.
  • Post in thread: What cable temperature to use for determining cable ampacity for sizing circuit breaker? 60C?

    What type of wire are you using, aka, THHN, RHW, etc?
  • Post in thread: Battery Cables math check

    Wire sizes are a little small given that NEC requires a 1.25% adjustment - but if you don't care about code compliance and or won't be inspected, the 2/0 "should" be OK. I'm assuming wire in conduit, not free air. All but 1 installation I've seen in the last 20 years or so wouldn't be...
  • Post in thread: Wooden battery rack and temperatures

    I have 12 batteries, arranged in 2 rows of six. I typically see a 8 degree F difference in battery temperature between the 2 rows with the upper being warmer.
  • Post in thread: System underperforming?

    Something is wrong with the 490V and 27.8A values. That's 13.62kW which greatly exceeds the 9kW of panels.
  • Post in thread: System underperforming?

    Looks like Matt found the issue!
  • Post in thread: Moving Inverter, 100' run Copper or Aluminum direct bury?

    I agree URD is direct burial, but over the years I have seen many direct burial cables fail because of nicks in the insulation. This is catastrophic when the conductors are aluminum. Can be damaged when installed, damaged from frost heave of sharp rocks, etc. Not to mention that a lot of folks...
  • Post in thread: System underperforming?

    And Ejimenez!!
  • Post in thread: Newbie Questions Regarding EG4 Solar Panel Wiring

    Finally had time to review the panel specs! You can run two strings of 8 panels into one PV input on each inverter, even given the -35F temperature! The PV input voltage limit is 500V. The 8 panels in series will exhibit an open circuit voltage of 466.5V at -35F. That would take you down to a...
  • Post in thread: Terminology.. phased power, apparent power, active power?

    Yea, it consumes 100w. The heat dissipation is interesting. My system has the batteries co-located with the inverters in a small 6'X8' shed, insulated to R11 in the walls, R32 "ish" in the ceiling, and no insulation in the floor. It sits on deck blocks, so it has around 12" of ground...
  • Post in thread: Moving Inverter, 100' run Copper or Aluminum direct bury?

    Sure, it is allowed, I just specify it be in pipe. Just a personal preference.
  • Post in thread: Fuse for 48v batteries to an all in one - off grids

    Also, the required fuse will most likely not be a standard value, so pick the next larger standard value fuse if reasonable.
  • Post in thread: Upgraded solar system, puzzled by the remaining limitation(s)?

    Is the inverter shutting down or are the battery BMSs shutting down?
  • Post in thread: Please could smebody check my wiring diagram

    Yea, everything else looks fine. PM me when tou get closer to building it. There are a lot of "gotchas" that pop up and I will be happy to help out further.
  • Post in thread: 2 AWG 2 wires vs 4/0

    Correct on the UL stuff, unless you can find it listed as a recognized wire type, like RHW, etc. A close cousin is DLO cable, which is RHH/RHW but it is more expensive. here's a linkhttps://1xtechnologies.com/dlo-cable/
  • Post in thread: Load Connection to Parallel Batteries

    It will take care of individual cell voltage imbalances but can't fix current imbalances resulting when the inverter is pulling large currents, aka powering a large load.
  • Post in thread: EG4-6500 losing clock and MPPT issues

    Both firmwares report U1 as 79.03 and U2 as 61.06. I have an open ticket on the issue. Tech support suggested I upgrade the firmware and am waiting on the cable to do so. BTW, the fault 71 issue is resolved as soon as I uplug the RS485 cable. Atleast at that point, I can restart both inverters...
  • Post in thread: EG6500Ex inverter does not see the batteries

    What type of batteries are in your system?
  • Post in thread: Code Compliance Question

    The authority having jurisdiction may have requirements in excess of whatever NEC has been adopted. I haven't seen the design you reference but there are a LOT of nuances in requirements. You may want an electrician experienced with solar to check the design. Are you certain you are subject to...
  • Post in thread: What cable temperature to use for determining cable ampacity for sizing circuit breaker? 60C?

    From the specs, it looks like you're using welding cable (RHW) or maybe DLO cable. I agree with Shimmy. Assume you have 75C terminations, so provide over current protection of 310A. That would allow a maximum inverter consumption of about 250A. You didn't mention inverter capacity or voltage...