timselectric
If I can do it, you can do it.
- Joined
- Feb 5, 2022
- Messages
- 19,099
You have to remove all bonding screws.The issue is whether or not the bonding relay in only one inverter
It should be sized for the current it will be carrying.What size of N would be required with 6 inverters?
Neutral sizing is always larger or equal to ground conductor.
This removes the grid input from the AIO.3 pole neutral switching where the system is SDS works too.
Which is what causes the issue in the first place.
Correct, if installed as an off grid stand alone system.These are sold as off grid inverters,basically standalone, thus the classification requires N-G bonding to be at the inverter.
But, that's not how they are being installed. Which is why this issue keeps coming up.
This issue only arises from using the grid input.