Zwy
Emperor Of Solar
That's the reason I believe common neutral is not supported. Hybrid inverters (can run with grid sharing) like the Deye/Sun Synch do not bond N-G under inverter power and rely on the N-G bonding at the service panel, that is why a contactor is needed to be installed if off grid or grid down operation is desired. The video was quite interesting, it clearly showed the inverter did not bond N-G.You may be on to something there. If the system is set up with a common neutral, the bonding screw must also be removed in order to ensure there is not a double bond. Since they don't document the bonding screw (and some distributors say removing the screw voids the warranty), maybe their assertion it is dangerous has a built-in assumtion the screw is in place
Remember the thread way back with the member using a Reliance transfer switch where the neutrals remained in the main panel? Only hots were moved to the transfer switch, as soon as it was turned on it tripped the breaker on the inverter. Of course the bonding screw was in place.
You know my stance on this subject, I prefer installing a 3 pole double throw in order to disconnect neutral from main service panel under inverter power and leaving the bonding screws in the inverters.