Source to buy quality wire ferrules?

edit-the victron publication reads “Use ferrules for all wiring connections,…”
That sounds logical.
Wouldn't thin, loose strands of copper be subjected to breakage under enough applied pressure? Better to cold weld them together in a ferrule me thinks.
 
Thanks. They still say “use ferrules” in the official documentation.

And there are at least a couple of ferrule statements in misc victron documentation.

I’ll keep looking for a “don’t use ferrules”. Weird that this isn’t settled.

Here's how I see it. This is a preponderance of the evidence situation:

1) The MPPT manual expressly states to use a fine strand wire with no mention of ferrules.
2) Guy says, no ferrules specifically on MPPT.
3) Video showing a Victron rep inserting fine stranded wire (not overwhelming evidence)
4) Given how the terminal works, I'm 100% certain that you get less contact area with a ferrule vs. a proper fine strand wire.

The Victron evidence to the contrary is a general statement about ferrule use in a general guide.

3.5 against ferrules
1 kinda for ferrules
 
Another view.

One officially published statement from Victron.

Versus some other informal stuff.

1 to 0.

Published documentation wins.

And I got the doc from a forum authority on Victron.
 
Another view.

One officially published statement from Victron.

Versus some other informal stuff.

1 to 0.

Published documentation wins.

And I got the doc from a forum authority on Victron.

Disagree.

One is a general guide that "highly recommends" and is also ambiguous AND context specific:

1680558808827.png

"Highly recommended" isn't mandatory.

Subsequent statement is ambiguous and context specific. They make an absolute statement; however, the use of "especially" indicates it's optional. Then they go on to discuss a specific type of connection where ferrule use is critical. NOTE: While these terminals have a screw, they are not "screw connectors".

AND THEN, they literally give instruction on how to insert a wire into a push connector WITHOUT A FERRULE!

1680559507754.png

The other is the manual specific to the component in question.

1680559002863.png

This is a singular directive with no option. If you use ferrules, you violate the directive.

If you use solid, you violate.
If you use coarse, you violate.
If you use rigid, you violate.
If you use ferrules, you violate.

Directive is repeated in the safety precautions link:
1680559282840.png
 
I don't think the directive to, "Use flexible, multi-stranded copper," precludes the use of ferrules. If they didn't want ferrules used, it would have been spelled out in the directives. Ferrules are optional, but highly recommended.
 
I used ferrules on my mppt’s no issues so far 6 months now
 
And push connectors are a different thing altogether. Fine stranded wire is particularly well suited to, and benefits from, ferrule use.
 
I used ferrules, but then again, my MPPT has just about ruined my batteries' ability to recharge themselves.
 
Guy is responsible in large part for the Victron documentation. If he's telling me something is wrong in the documentation, or it needs to be updated, I'm going to listen.

Worth nothing that I too value VWE as it's the 5th link in my sig and has been for a long time, but the doc itself indicates that it's intended as a guide.
 
These days, the title "engineer" gets thrown around to anyone that can rub two brains cells together. Heck, my title might be Principle Software Engineer right now. I don't keep track of my title so I'm not really sure. It used to be that to have an "engineer" title you had to be an actual engineer with a license from a state board.
 
He's been a Victron employee for at least 5 years.

Join the Victron Professional site. He does a lot of the training videos.


If you work for Victron and are on Community, you get:

1680579732334.png


What does this link tell you?

 
I appreciate you chiming in Brad.

Is that across the board or dependent on the clamp mechanism in this charge controller?

I was under the impression that there was an advantage to the ferrule with some connection types.
 
That AlaskanNoob guy....shining light through ignorance yet again.

Guy said he was going to come up with a better explanation so hopefully he's working on some documentation.
 
I appreciate you chiming in Brad.

Is that across the board or dependent on the clamp mechanism in this charge controller?

I was under the impression that there was an advantage to the ferrule with some connection types.
Sure there are but not with the type of connections we have with the Victron solar controllers and DC to DC converters.
 
What's a ferrule? :p

Seriously , I would never consider using ferrules on the MPPT. I don't know the name for those types of terminals, but they effectively maximize contact area between the terminal and stranded wire. Putting a ferrule in them would reduce contact area.


1.2. Wiring safety precautions • Use flexible multi-stranded copper cable for the battery and PV connections. • The diameter of the individual strand of the cable used should not exceed 0.4mm (0.016 inch) or have a surface area exceeding 0.125mm² (AWG26). • The maximum operating temperature is 90°C (194°F). • • A 25mm² cable, for example, should have at least 196 strands (class 5 or higher stranding according to VDE 0295, IEC 60228 and BS6360). An AWG2 gauge cable should have at least 259/26 stranding (259 strands of AWG26). Example of suitable cable: class 5 “Tri-rated” cable (it has three approvals: American (UL), Canadian (CSA) and British (BS)). • In case of thicker strands the contact area will be too small and the resulting high contact resistance will cause severe overheating, eventually resulting in fire. See below figure for examples of what cable to use and not to use.
View attachment 142745


I would say this is consistent with Guy's assertion.
The Luxpower 12k inverter manual specifically says to use wire ferrules on the MPPT terminal connections. these connections are close together in space and I assume they want to reduce the risk of ARCing. However, the battery terminals do not say to use ferrules, but the fine stranded wire is compression screwed, not using a hole through lug for the connection.
 