EG4 18kPV Q+A general thread

They apparently mention it in the latest 1.3 manual I just downloaded. And I do mean mention. Starting The Inverter 6.4.1 Item 2. and 6.4.2 Item 3, shutdown. No picture Vague reference because obviously everybody knows . . . "
Turn on PV isolator switches between the inverter and the array and then on the side of the inverter". (emphasis mine) Frankly, I was just being acidic, I guessed that is what it must be, but at first I thought it was like some sort of master power control. And unless someone can cite some other chapter and verse I missed, that is the only reference to any of the left side switches. The RSD button is not formally mentioned, though they do talk about a transmitter behind the main board. Just sloppy, you have drawings and pictures of all the rest of the stuff, but the big giant switch on the side that disconnects the PV inputs? nah! If you have a big giant rotary switch and a button on the side of your cabinet, one would think it would get a paragraph and drawing/picture in the PV section.

Before telling someone to "Read the Manual" looking for a needle in a haystack, I would suggest citing chapter and verse to be helpful. You know like "If you download the latest PDF they reference it briefly on page 62 in the startup shutdown procedures". An then if one were all knowing perhaps add in useful exposition, "The RSD button does something, probably shuts down the PV input in a different way" , or "Suppport says ..." YMMV.

IMG_1513.jpeg


It does look similar to the Sol-Ark:

IMG_1512.jpeg
 
It says in eg4 warranty statement that they basically don't take any responsibility for your lack of knowledge. That they recommend having a licensed trained professional installer install this equipment (not quoted as the exact wording). So if you can't figure out this Big Giant sloppy switch, you better just hire some one who can so you don't kill some one. Then that installer can explain all your questions about the unit.
 
Since this is a Q+A thread about this specific device, they need to fix the book, not everyone has a Sol-Ark manual laying around to compare notes.

BTW, would that be anything like hiring a licensed electrician an having him install mis-labeled equipment? how about a licenced Pest Control operator, here's a bottle of chemicals, it kills bugs, doesn't have a label, but your licensed so you know everything right? I've been doing electronics since the tube days, how about a 6L6 and wind your own coil for a transmitter? If I can't figure it out, neither will the vast majority of licensed installers. This is a brand new product, the manual needs to be better, and should describe all the components of the device period. Licensed pilots flew 737Max's into the ground because the manuals and instructions were not clear. Do not make excuses for shoddy documentation.

Shout-out to Danke. The Sol-Ark similarity is interesting to an extreme. That was actually the unit I was looking at when I opted for the 18K. And we note a simple picture labeling the various knobs and such, that are very similar... What if they weren't? I know 'Licensed Installers' don't always read manuals on new products they've never seen but they should still refer to them. I know in the last 50 or so years, I've never had a licensed installer try and blow smoke up my rear after they installed something incorrectly. But it says here in the manual, ....

Documentation is a lot like sex. When it's good it's wonderful, and when it's bad, it's better than nothing.
 
I still ended up using the Chargeverter in my plan because there doesn't seem to be a way to have any AC input simply used to throw DC at the battery bus. This is really annoying, since the needed circuitry is in the box. When my A/C unit kicks on it causes a complete blip that trips the UPS's on my electronic gear. It's a 4T unit, low end Goodman. I will put a soft-start kit in it to see if it helps reduces the starup draw. Someone stole my fancy recording fluke on a job but the pull must be very extreme. It dims the lights directly from the 150A grid, but it basicially kicks down to nothing attached to the inverter. The a/c unit is only a year old. The house is early 70's block, and they used aluminum wiring up the the roof for the A/C. (And the HWH and the Dryer). I've never been a fan of aluminum, but the run up to the roof thru the attic is a bear. I'm wondering if running some #6 copper THHN would help as well, it looks to be #6 aluminum on a 50A breaker. I already swapped out the HWH for copper, the dryer is a more problematic run as well.

I've not done a full stress test yet either. i have two units in parallel, Next test will start an EV charge @24A sustained, and see about getting the load to spike ovver 60 or so.
 
I still ended up using the Chargeverter in my plan because there doesn't seem to be a way to have any AC input simply used to throw DC at the battery bus. This is really annoying, since the needed circuitry is in the box. When my A/C unit kicks on it causes a complete blip that trips the UPS's on my electronic gear. It's a 4T unit, low end Goodman. I will put a soft-start kit in it to see if it helps reduces the starup draw. Someone stole my fancy recording fluke on a job but the pull must be very extreme. It dims the lights directly from the 150A grid, but it basicially kicks down to nothing attached to the inverter. The a/c unit is only a year old. The house is early 70's block, and they used aluminum wiring up the the roof for the A/C. (And the HWH and the Dryer). I've never been a fan of aluminum, but the run up to the roof thru the attic is a bear. I'm wondering if running some #6 copper THHN would help as well, it looks to be #6 aluminum on a 50A breaker. I already swapped out the HWH for copper, the dryer is a more problematic run as well.

I've not done a full stress test yet either. i have two units in parallel, Next test will start an EV charge @24A sustained, and see about getting the load to spike ovver 60 or so.
A soft start is the best option. They are well worth the money.
 
I just put a soft start on mine. Reduced to 22a on startup. No flicker.

Anyone know if you can add say a lv6048 to the grid side of this inverter? Say I wanted a tad more capacity but used off grid without buying another 18kpv? Thats out of my budget.
 
I just put a soft start on mine. Reduced to 22a on startup. No flicker.

Anyone know if you can add say a lv6048 to the grid side of this inverter? Say I wanted a tad more capacity but used off grid without buying another 18kpv? Thats out of my budget.
Only if you can guarantee that it will never export to the 6548. That would damage the 6548.
 
I still ended up using the Chargeverter in my plan because there doesn't seem to be a way to have any AC input simply used to throw DC at the battery bus. This is really annoying, since the needed circuitry is in the box. When my A/C unit kicks on it causes a complete blip that trips the UPS's on my electronic gear. It's a 4T unit, low end Goodman. I will put a soft-start kit in it to see if it helps reduces the starup draw. Someone stole my fancy recording fluke on a job but the pull must be very extreme. It dims the lights directly from the 150A grid, but it basicially kicks down to nothing attached to the inverter. The a/c unit is only a year old. The house is early 70's block, and they used aluminum wiring up the the roof for the A/C. (And the HWH and the Dryer). I've never been a fan of aluminum, but the run up to the roof thru the attic is a bear. I'm wondering if running some #6 copper THHN would help as well, it looks to be #6 aluminum on a 50A breaker. I already swapped out the HWH for copper, the dryer is a more problematic run as well.

I've not done a full stress test yet either. i have two units in parallel, Next test will start an EV charge @24A sustained, and see about getting the load to spike ovver
Well, I apologize for my comment to ya. Looks like I might have some of the same issues hooking up grid to charge and share loads if some one don't figure this thing out, as I planned to use it for. Last thing I want is for any thing getting exported to the grid.
 
Last edited:
The chargeverter is the perfect solution.
My system is completely off grid.
But I can use the grid, generator, or any other source for backup, through the chargeverter. Because the chargeverter is my only connection to the grid. It removes a lot of the issues that are created by connecting to the grid.
Ground loops
N/G bonding
Backfeeding
Ac charging
And allows the generator to work at peak efficiency.
 
I just put a soft start on mine. Reduced to 22a on startup. No flicker.

Anyone know if you can add say a lv6048 to the grid side of this inverter? Say I wanted a tad more capacity but used off grid without buying another 18kpv? Thats out of my budget.
From what i've read you're better off connecting another inverter to the generator port for AC coupling.
 
From what i've read you're better off connecting another inverter to the generator port for AC coupling.
Would that add additional wattage over the 12kw? Another words would it “blend” well like it pulls from the grid port now?

Still have about .1-.2kwh export a day. Have not updated the firmware yet to see if that solves it. Inverter was put in only 2 weeks ago so Im assuming it’s fairly up to date.
 
The chargeverter is the perfect solution.
My system is completely off grid.
But I can use the grid, generator, or any other source for backup, through the chargeverter. Because the chargeverter is my only connection to the grid. It removes a lot of the issues that are created by connecting to the grid.
Ground loops
N/G bonding
Backfeeding
Ac charging
And allows the generator to work at peak efficiency.
Are you using this with the 18kpv?
 
So my panels go on the roof Saturday. I've been doing load testing and these 18K's seem to be very robust thus far. The soft-start improved the dip but did not eliminate it; now it just blinks. The highest (sustained) draw so far has been just under 60A. There is a long story behind the A/C unit on the roof, but it will at some point be replaced with mini-splits. I had started insulating the walls in the room this stuff is in (for the inverters I ripped out), and since I own a couple of portable A/C's (see long story ;)... To kick this off the plan was to leverage the smaller one to cool the room (roughly 8x11), setting it to a relatively high value (90 - 95, whatever it will let me go up to). The room was ~108F when I got home at 1730, I kicked on the inverters against the batteries to do some load shifting for a couple of hours (1300-2000 is peak). A/C was running fans did not kick on, at about 2700W/unit. Both units were uncomfortably warm to the touch on the cabinet (misplaced my temp gun) but not blister producing at all. It's going to hit 120 in that room from time to time, July/August without A/C , but I wonder how much these guys can actually deal with. I think the spec sheet lists these at -25C to 60C (140F), derated > 45C (113F). I'm not sure I might not be better off with a vent fan. That is some serious temperature range. The question would be how much we ar gonna 'de-rate' it. Manual doesn't mention it specifically but 48C(120F) is still pretty far under the max. I've never seen it over 123F here.

I'd welcome any thoughts on the temperature. Looks like 30K of batteries dropped about 40% in 2 hours. This might be affected by temp more than the inverters. On a better direction I have the control system kicking the relay for the chargeverter daily at 2005. It is set at 75A. It actually charges the batteries a few percent between 2005 and 0700 (When I turned it all off) This is going to be interesting, The modbus RS485 on the unit is set to 19200 according to the manual. All the other stuff I have is 9600. The problem with USB dongles is the order of enumeration is sometimes impossible to predict. I want finer control over turning the A/C charging on. I'll figure something out, maybe just grab onto the battery bus, it's 9600 I think. I set my other modbus sensors starting at ID 10.
 
So my panels go on the roof Saturday. I've been doing load testing and these 18K's seem to be very robust thus far. The soft-start improved the dip but did not eliminate it; now it just blinks. The highest (sustained) draw so far has been just under 60A. There is a long story behind the A/C unit on the roof, but it will at some point be replaced with mini-splits. I had started insulating the walls in the room this stuff is in (for the inverters I ripped out), and since I own a couple of portable A/C's (see long story ;)... To kick this off the plan was to leverage the smaller one to cool the room (roughly 8x11), setting it to a relatively high value (90 - 95, whatever it will let me go up to). The room was ~108F when I got home at 1730, I kicked on the inverters against the batteries to do some load shifting for a couple of hours (1300-2000 is peak). A/C was running fans did not kick on, at about 2700W/unit. Both units were uncomfortably warm to the touch on the cabinet (misplaced my temp gun) but not blister producing at all. It's going to hit 120 in that room from time to time, July/August without A/C , but I wonder how much these guys can actually deal with. I think the spec sheet lists these at -25C to 60C (140F), derated > 45C (113F). I'm not sure I might not be better off with a vent fan. That is some serious temperature range. The question would be how much we ar gonna 'de-rate' it. Manual doesn't mention it specifically but 48C(120F) is still pretty far under the max. I've never seen it over 123F here.

I'd welcome any thoughts on the temperature. Looks like 30K of batteries dropped about 40% in 2 hours. This might be affected by temp more than the inverters. On a better direction I have the control system kicking the relay for the chargeverter daily at 2005. It is set at 75A. It actually charges the batteries a few percent between 2005 and 0700 (When I turned it all off) This is going to be interesting, The modbus RS485 on the unit is set to 19200 according to the manual. All the other stuff I have is 9600. The problem with USB dongles is the order of enumeration is sometimes impossible to predict. I want finer control over turning the A/C charging on. I'll figure something out, maybe just grab onto the battery bus, it's 9600 I think. I set my other modbus sensors starting at ID 10.
Do you have a basement?
 
Do you have a basement?
Nope, Three sides block on slab Garage/West side has meter, Co-opted utility room for the project. A/C will not keep room cool, it keeps shutting down for 5-10 minute intervals every time the main A/C cuts on every 10-15 minutes and browns out the service. This is a significant problem. I might just stick it on the grid, and get creative with something to turn it on. Need to get this going, then I'll figure outhow to handle the A/C issue. Not sure what I can do
 
Nope, Three sides block on slab Garage/West side has meter, Co-opted utility room for the project. A/C will not keep room cool, it keeps shutting down for 5-10 minute intervals every time the main A/C cuts on every 10-15 minutes and browns out the service. This is a significant problem. I might just stick it on the grid, and get creative with something to turn it on. Need to get this going, then I'll figure outhow to handle the A/C issue. Not sure what I can do
Use grid peak shaving feature, it will act the grid as a transformer when there is a sudden big load on the inverter, set it to 0.1 which is the inverter will always draw 100 watts from the grid and the inverter will take the rest of the load.. i been using this and its been working well for My needed.
 