Very nice! Good do you have the generator hooked up?Just around 3 1/2 months here. Over 6Mwh solar and almost 7Mwh thru the inverter.
View attachment 167424
Very nice! Good do you have the generator hooked up?Just around 3 1/2 months here. Over 6Mwh solar and almost 7Mwh thru the inverter.
View attachment 167424
No generator hooked up at this time.Very nice! Good do you have the generator hooked up?
Critical load panel here as well but main is empty other than 3 circuits. I receive similarly explained bills where I use for say 1 month Supply charge of 2.08 and Delivery of 8.93 = 11.01 or another Month Supply 7.75 and Delivery 12.68=20.43 Not really fair but pay it as insurance to keep the grid use when needed. Your situation looks like their coming up with ways to comp some of there overhead but if you except it you'd be legal to use or feed back grid and use it as a supplement. It would be great to use the 18kpv to it's full potential with all it's bells and whistles but is still a great inverter even if used just off grid.I have mine setup as a critical load panel. I only turn on grid if my batteries are low. My Power company put me on the "wait list " for a "Interconnection Agreement". Once approved, if I even accept their terms...I'd need to pay the $10 monthly fee for a 2nd meter and a monthly $22 manual billing fee. Additionally the only benefit would be using the grid as a battery. (They pay zero cents per kWh)
the utility is pushing for approval from the utility commission to allow billing for distribution fees for all kWh pushed or pulled from the grid.
Example my kWh rate is 11 cents and distribution cost around 9 cents per kWh. With each kWh I feed into the grid, I can get back for free.
But if their request is approved I would pay 18 cents per kWh in distribution cost.) Their argument is the distribution network is being used but not paid for....so while the energy is free the service provided by the network of cables and transforms isn'. I see on my bill examples similar to your explanation as on my bill shows 1 month supply being 2.08 and delivery 8.93 equal to 11.01 or another mo., supply of 7.75 and delivery of 12.68 equal to 20.43.I don't bother to complain just pay.
This!Folks, you cannot call Deye and ask them to private label an inverter for you in the USA. that may be limited to SolArk. I believe you can call Solis, Growatt, Luxpower and some others and they will private label you an inverter.
So maybe the forum should have a design your ideal inverter thread. Set the final specs and get people to commit to buying it and doing community support. Savings could be in the thousands.
Let's start: Inverter Output AC 240/120 sizes 8k, 12k and 16k. Parallel up to 3 inverters (equals 200 amps). Built in ATS, generator support, high voltage and low voltage battery support, 4 MPPT's at 20 amps each up to 600 volt DC input. Max PV input equals 36 kW. AC coupled too. Breakers included, wifi and cellular dongle. Included 120 amp or 180 amp battery charger, NEMA 4, convection cooling, floor mount or wall mount, full software support, all other standard certifications and features such as UL1741, CEC compliant and, UL9540 and rapid shutdown.
If there was a commitment to 1,000 units of these, the price landed would come in at probably 3K or less. Sort of like an inverter kickstart.
This kind of project means larger heat sink, MOSFETS, etc. But nothing that is not already being done in the larger 3 phase utility and commercial inverters.
FWIW, if you want to UL it then you need to focus on a single configuration like 16kW to keep the cost manageable. The UL littany is about $100k per inverter all-in (maybe only $80k for UL of subsequent models on the same platform).Let's start: Inverter Output AC 240/120 sizes 8k, 12k and 16k. Parallel up to 3 inverters (equals 200 amps). Built in ATS, generator support, high voltage and low voltage battery support, 4 MPPT's at 20 amps each up to 600 volt DC input. Max PV input equals 36 kW. AC coupled too. Breakers included, wifi and cellular dongle. Included 120 amp or 180 amp battery charger, NEMA 4, convection cooling, floor mount or wall mount, full software support, all other standard certifications and features such as UL1741, CEC compliant and, UL9540 and rapid shutdown.
Good pointFWIW, if you want to UL it then you need to focus on a single configuration like 16kW to keep the cost manageable. The UL littany is about $100k per inverter all-in (maybe only $80k for UL of subsequent models on the same platform).
Honestly though the EG4 18kPV is close enough for me. What is a much bigger challenge to me is the battery situation. I want a 60kWh single forklift box with integrated everything that is designed to go in a residential garage (ideally without fire sprinklers). I want something that the fire inspectors and the city can't complain about since it is a UL box listed for the application.
This should read as “some firmware iterations have 98% of these features functional”The EG4 18k and Solark 15K and clones already have 98% of all these features covered.
?This should read as “some firmware iterations have 98% of these features functional”
UL 9540 limits you to 20kWh in a single rack. Doesn't make sense to make a large box for 3 racks that are 3 feet apart.Honestly though the EG4 18kPV is close enough for me. What is a much bigger challenge to me is the battery situation. I want a 60kWh single forklift box with integrated everything that is designed to go in a residential garage (ideally without fire sprinklers). I want something that the fire inspectors and the city can't complain about since it is a UL box listed for the application.
By rough calculations, you could have a Nema-12 box about 30" wide x 18" deep x 76" high that integrates 60kWh of battery (64 304Ah cells), inverter electronics from an existing design, all the needed circuit breakers, and bypass breakers (actually a panelboard if it had side access) in a separate compartment. If you wanted to make it stackable for battery or inverter there are a few elegant ways to do it while limiting field work.You are going to have to commit to at least 100,000 units to even attempt to talk to manufacturers.
The EG4 18k and Solark 15K and clones already have 98% of all these features covered.
I thought there was a path around that for LFP, but there are still some inconsistencies between NFPA and UL. The key as I read it was that it be listed as a single unit and tested in accordance with 9540A.UL 9540 limits you to 20kWh in a single rack. Doesn't make sense to make a large box for 3 racks that are 3 feet apart.
FantasticToday i reached 75 days after installing the 18kpv and i’m lucky have round numbers:
75 days
4000kWh Solar Production
5400kWh Consumption through the inverter
Im in love with this thing, doesn’t get old
I still haven’t been able to grid tie, when i finally get that done, production will average much higher because usually the batteries are full by noon and there is a lot wasted energy from 12pm-5pm
I have my neighbors charging their Tesla twice a week at home because its just sad to not have all that energy used.
20 x 460w solar Panels = 9200w
14 x 550w solar Panels = 7700w
16700w total
The max pv input ive seen for more than 3 minutes is 11,000w… thats 34% less than nominal value. Is this normal? Other than cleaning my solar panels with ive already done 1 month ago. Any recommendations to get better results? My panels are pointed perfectly to south and at the proper angle also, so Ive got that covered.
Thank you all
View attachment 170901
(18.4483419, -69.9480740)Fantastic
What is your latitude? What type of panel?
Oh strange, you should have a bit more output. Are they used panels? How are they wired? How are they connected to the 18K? Can you post your PV data from a sunny day on here?(18.4483419, -69.9480740)
Santo Domingo, Dominican Republic
460w Peimar mono-crystalline
550w JaSolar mono-crystalline