In this case, 65v (Enhanced grid support) will do the opposite of what it sounds like he's trying to do. Enhanced grid support prioritizes the battery and keeps them fully charged, and then *excess* sells back to the grid (or main panel). Since he's not selling to the grid, enhanced grid support would essentially do exactly whats happening now.. batteries full, and PV array stops producing because there is nowhere for the power to go.I might have borked my advice and 65 volts is actually the key to enable grid support, not 64. @n2aws is more expert than me though.
I'll say again if you want a shortcut to make it do something, flip the AC input breaker and create a grid outage. But try 65 first.
Ahh, I think we're crossing some of our wires.Sorry n2aqs. I thought I provided what you were looking for. The only "advanced" I see after the "status" is under CONFIGURATION. From there I seem to get a lot of individual statements i can open.
View attachment 180555
Under status I don't see advanced. Please know that I use 1.14 of the firmware and that my be the reason.
I have 300+ Voltage at both MPPT's so no breaker is tripped. The disconnect switch is not tripped as the entire system goes black when that o cures. I am really happy for any help I can get here and you n2aws really do. What can I provide?
Ahh, I think we're crossing some of our wires.
From the status page of the inverter, can you go to "print" (in your browser). and print to PDF. Attach it to this thread. That will give us a single point of reference for how everything on your inverter is configured. Note, it needs to be from your inverter page, not an MPPT page.
The Status pages for the inverter and both charge controller was posted at 11:13am. Is this not what you were asking for?Ahh, I think we're crossing some of our wires.
From the status page of the inverter, can you go to "print" (in your browser). and print to PDF. Attach it to this thread. That will give us a single point of reference for how everything on your inverter is configured. Note, it needs to be from your inverter page, not an MPPT page.
To n2aws I have been following this thread from the beginning as I have also have a XW+ and plan to change to LIFEPO when replacement is necessary. I really appreciate the info you and others are supplying in such detail,
Thanks, wayne cook
Perfect, thanks. and totally my fault. It was the configuration I wanted.n2aws - is this what you wanted. Or is it the CONFIGURATION of all the set up?
No worries.Thank you n2aws - now the sun is gone for today. I will try tomorrow to set the Inverter to Standby Mode.
I'm honestly confused. your screenshots showed your batteries at 54.4 volts. you mentioned having 2 banks of batteries in your first post. your critical loads panel is drawing ~1k, how have you gone from 54.4v to 48v in the last couple of hours? I've only got 1 bank of batteries, and am trying to test something (for another user) and intentionally trying to get my batteries to 5% SOC.. after 4 loads of laundry running the dryer, I'm at 56%I did it - and the batteries are at 48 Volts and the system seems to go back to the grid when that happens and back to the batteries again after a few seconds. That does not seem to good either.So it keeps switching between charging the batteries and taking from the batteries seconds apart. How do I stop that?
320ah of battery should still be 15kwh of energy. at a 1,000 watt load, you should have 15 hours. Obviously, I don't know if that 1kw load is consistent or spikes to 5k or something.. but the fact that you went from 54.4v to 48v in such a short period of time would make me suspect some cell imbalance. But, thats likely an issue for some other time. If the batteries really are dropping to 48v... and you have the grid support voltage set at 52v, that would explain the behavior you are seeing. when the voltage sags below 52v, it'd stop supporing the loads and go to AC passthrough. After the voltage sag subsides and the voltage climbs back over 52v.. it'd enable peak load shaving again.Yes I have 2 banks of older lithium batteries each at 160 AH connected in parallel. I think that due to the age they discharge quite fast. I use 2 separate BMS system to control them. The BMS is only available to my iPhones for setup and control.
looks like a mix of 15s and 16s? green is 15s. blue is 16sWait wut?
Why do you have 15S batteries?
Not sure what to make of this but here are some numbers i was wondering about.
Charging to 54.4V = 3.62Vpc
48V = 3.2Vpc
15S +1 orphanblue is 16s