18 month DIY project finally done: 39kW inverter power off grid system

I also monitor very closely the battery situation. All 12 batteries are very close regarding their SOC and voltage. Also, while charging/discharging they all take/give the same wattage of power. Here is an example while charging with 7.6kW:
1714668935194.png 1714668950776.png 1714668977385.png

I also monitor the max. highest cell delta over all batteries in my smart home system. The following chart shows the max. delta over the last 5 days (SolarAssistant only gives me the max/min/average cell delta per battery and not for each cell inside each battery, the these are all max values):
1714669080826.png
The max. cell delta will usually stay below 30mV and only rises for a short time up to 150mV just before they are fully charged in bulk mode (with about 0.15C) and while keeping them full for the rest of the day the max. delta will be between 60mV and 90mV (float?). As soon as the batteries gettting discharged again (from around 100% SOC), the max. delta will again drop below 30mV. I think this behavior is ok - but not 100% sure! As far as I understand, it's ok if the max. cell delta will be much higher just before bulk charging ends...

This is the battery temperature chart over the last 5 days:
1714669472404.png

Update
Btw. I'm using 55.2V absorption charge voltage and 53.6V float charge voltage
 
Last edited:
Btw. I'm using 55.2V absorption charge voltage and 53.6V float charge voltage
This is why they "appear" to be well balanced.
You are staying in the flat part of the charging curve.
There shouldn't be any delta variation, unless a cell is failing.
 
Last edited:
I would like to thank everyone!
Without this DIYSOLARFORUM and your help, suggestions, answers, tips, etc. the project would not have been a success.

Everything is possible with a good community behind you - share and learn from each other!

A very big thank you (y):)
 