In the diagram shown, If the critical load panel tried to draw more than 70A from the main panel, the 70A breaker in the main panel would trip. However, the design center of the system shown assumes a smaller total load from the Critical load panel so that would normally not happen unless there was a fault.
The question being asked (as I understand it) is whether the 200A breaker in the existing Critical load panel can be left in place and therefore not have overcurrent protection at that point in the circuit. At first glance, it seems like it would be OK. This circuit has protection from grid current because of the 70 breaker in the main panel. Since the load breaker in the inverter is 200A, it does not offer additional protection. Consequently, there is no over-current protection breaker for current from the inverter. The inverter is self-limiting so if the current got too high it would shut down, but I don't know if the NEC would consider that adequate.
The question being asked (as I understand it) is whether the 200A breaker in the existing Critical load panel can be left in place and therefore not have overcurrent protection at that point in the circuit. At first glance, it seems like it would be OK. This circuit has protection from grid current because of the 70 breaker in the main panel. Since the load breaker in the inverter is 200A, it does not offer additional protection. Consequently, there is no over-current protection breaker for current from the inverter. The inverter is self-limiting so if the current got too high it would shut down, but I don't know if the NEC would consider that adequate.