I have come across a challenge with my borehole system:
Initial power comes from 8 x 300 watt high voltage panels, (2 strings of 4 panels in series (300vdc) connected in parallel). Total output 300vdc and 2.4 kW in full sun. This powers a TopSolar mppt inverter which is rated at 300va and 230vac output. This charges 2 x LiFePo4 battery packs at 24vdc and 5 kWh capacity which means I have power 24/7.
This in turn powers a VEGA DY220SL photovoltaic pump controller (at 230vac input) through an isolation relay operated by a float switch in my water storage tank. The VEGA unit runs a 230vac 3∆ borehole pump rated at 0.75 kW (1 HP).
The VEGA unit consumes 1350 watts soft start (single phase) which should relate to 1.5 kW ie; within the capacity of the TopSolar (3,000va = 2.55 kW). However, the TopSolar unit is actually running at a constant 105% (overload) = 2.68 kW.
If I run an electric kettle (1.5 kW resistive load) on the TopSolar unit it reads 56% load and no overload.
Please can anyone explain why there is this huge difference? I know it must be due to a reactive load as opposed to a resistive load but I don't know why. Or if I can resolve this issue. ie; just buy a bigger primary inverter or is there some way to make the TopSolar unit see the VEGA unit differently.. without running a constant overload.??
Best regards and Many thanks. James Leenders
I have come across a challenge with my borehole system:
Initial power comes from 8 x 300 watt high voltage panels, (2 strings of 4 panels in series (300vdc) connected in parallel). Total output 300vdc and 2.4 kW in full sun. This powers a TopSolar mppt inverter which is rated at 300va and 230vac output. This charges 2 x LiFePo4 battery packs at 24vdc and 5 kWh capacity which means I have power 24/7.
This in turn powers a VEGA DY220SL photovoltaic pump controller (at 230vac input) through an isolation relay operated by a float switch in my water storage tank. The VEGA unit runs a 230vac 3∆ borehole pump rated at 0.75 kW (1 HP).
The VEGA unit consumes 1350 watts soft start (single phase) which should relate to 1.5 kW ie; within the capacity of the TopSolar (3,000va = 2.55 kW). However, the TopSolar unit is actually running at a constant 105% (overload) = 2.68 kW.
If I run an electric kettle (1.5 kW resistive load) on the TopSolar unit it reads 56% load and no overload.
Please can anyone explain why there is this huge difference? I know it must be due to a reactive load as opposed to a resistive load but I don't know why. Or if I can resolve this issue. ie; just buy a bigger primary inverter or is there some way to make the TopSolar unit see the VEGA unit differently.. without running a constant overload.??
Best regards and Many thanks. James Leenders