I'm running a Schneider 6448 (6.4k / 48v.) inverter. Two MPPT 600's. Batteries and Grid Tied (to sell back).
I had 22 of my new 400 watt panels working (11 to each controller). I've been seeing a high of 6.31Kw on the inverter at what I would call peak sun (around noon).
That as calculated gave me just under 600 v. open circuit using the multiplier for cold weather. Now that it's warming up with nighttime lows in the 50's, I thought
I would hook up two more panels and check the results. So 12 and 12 on a string. I had 28 panels on the array with the last 6 not connected.
To my surprise, the next two days watching the inverter display, the highs I would be seeing was 6.29 to 6.31. It stayed there from about 11am to 2pm.
You can get up to 10k out of that inverter for a short period of time. Thinking it was 20-30 minutes. Sliding scale to the 6.4k where it's continuous.
I figured, adding another 800 watts I would now see about 7k on the inverter. It never went higher then 6.31.
I have 9600 watts of panels. My MPPT's were at one point harvesting 3226 and 4322. Combined that's 7548. Inverter only showing 6.3k. It;s in grid sell status.
I know there are losses. This is about 20%.
Can the 6448 only accommodate 6.4k of panels? The excess the MPPT's were showing selling back to grid?
Does adding these panels only give me more power generation before and after peak sun where I max out at 6.31k?
Not the result I was expecting having been told by a Scheinder installer he regularly adds more panels. But maybe this is the result
of doing that, I just was expecting to see more inbound watts displaying on the inverter.
I had 22 of my new 400 watt panels working (11 to each controller). I've been seeing a high of 6.31Kw on the inverter at what I would call peak sun (around noon).
That as calculated gave me just under 600 v. open circuit using the multiplier for cold weather. Now that it's warming up with nighttime lows in the 50's, I thought
I would hook up two more panels and check the results. So 12 and 12 on a string. I had 28 panels on the array with the last 6 not connected.
To my surprise, the next two days watching the inverter display, the highs I would be seeing was 6.29 to 6.31. It stayed there from about 11am to 2pm.
You can get up to 10k out of that inverter for a short period of time. Thinking it was 20-30 minutes. Sliding scale to the 6.4k where it's continuous.
I figured, adding another 800 watts I would now see about 7k on the inverter. It never went higher then 6.31.
I have 9600 watts of panels. My MPPT's were at one point harvesting 3226 and 4322. Combined that's 7548. Inverter only showing 6.3k. It;s in grid sell status.
I know there are losses. This is about 20%.
Can the 6448 only accommodate 6.4k of panels? The excess the MPPT's were showing selling back to grid?
Does adding these panels only give me more power generation before and after peak sun where I max out at 6.31k?
Not the result I was expecting having been told by a Scheinder installer he regularly adds more panels. But maybe this is the result
of doing that, I just was expecting to see more inbound watts displaying on the inverter.