so this system that in the house we not long purchase as an Growatt which I been told is fault,
Checking the sunny boy inverter it show it putting in around 10kwh at the most per day .
I been quoted for a givenergy Gen 2 at 9.5 kWh
Or
All in one 13.5kwh
As my panels are only max at 10kwh is there any point in putting in a 13.5 gen set as the panel as I see it will never put enough in to fully charge them ,
Or am I missing something and if so what .
Thanks