My system has a single EG4 LLv2 48V battery.
For safety, I was considering adding a battery fuse in addition to my main breaker off the battery (not the battery switch/breaker). as I have seen recommended.
After doing some calculations based on my max inverter surge watts/current, additional constant DC loads, BMS short circuit current, etc, I thought 125 or 150 amps would be a good choice, class T.
But then I remembered that the battery switch is itself a breaker. Here it is:
This appears to be this exact breaker, available from SS separately:
So the question is, do I still need/want a fuse? If so, only for a quicker trip/blow when I hit that current? Or am I needlessly over thinking this? Thanks for any thoughts.
For safety, I was considering adding a battery fuse in addition to my main breaker off the battery (not the battery switch/breaker). as I have seen recommended.
After doing some calculations based on my max inverter surge watts/current, additional constant DC loads, BMS short circuit current, etc, I thought 125 or 150 amps would be a good choice, class T.
But then I remembered that the battery switch is itself a breaker. Here it is:
This appears to be this exact breaker, available from SS separately:
Nader DC Circuit Breaker | 48V 125 Amp
Signature Solar provides solar panels, off-grid solar systems, grid-tie, and hybrid systems. Quality solar inverters, bifacial solar panels, complete solar kits, solar batteries. Featuring brands such as EG4 Electronics with their solar battery, LifePower4 and EG4 LLifePower4 and EG4 LL
signaturesolar.com
So the question is, do I still need/want a fuse? If so, only for a quicker trip/blow when I hit that current? Or am I needlessly over thinking this? Thanks for any thoughts.