Hello everyone! Been researching and trying to figure the answer to this out; however, I cannot. As each document someone has or video watched leaves out one step, the wire size of the interconnected batteries.
Here is what I will be doing:
2 - 2.4wkh AIO inverters (MPP 2424)
4 - 24v 100ah batteries
The manual for the inverts state a 125A fuse between the batteries and the inverter...which makes sense (2400/24*1.25)
The manual then states to run the inverts in parallel, to have 400ah on the batteries and the bank connected to both inverters...ok, do the math again (4800/24*1.25 = 250ah)
Since the 250ah is the max, should I gauge the interconnection on this figure, or the max amp hours of the battery bank (400, well 500 since the 1.25)?
My assumption based on what I can find (which is nothing really) would be the max current, so 250ah or 4/0 wire.
Second question, the batteries will connect to a busbar and then from the busbar to the inverter, I would go with the wire for 125a, 1/0 (the manual says 2agw).
Thanks!
Justin
Here is what I will be doing:
2 - 2.4wkh AIO inverters (MPP 2424)
4 - 24v 100ah batteries
The manual for the inverts state a 125A fuse between the batteries and the inverter...which makes sense (2400/24*1.25)
The manual then states to run the inverts in parallel, to have 400ah on the batteries and the bank connected to both inverters...ok, do the math again (4800/24*1.25 = 250ah)
Since the 250ah is the max, should I gauge the interconnection on this figure, or the max amp hours of the battery bank (400, well 500 since the 1.25)?
My assumption based on what I can find (which is nothing really) would be the max current, so 250ah or 4/0 wire.
Second question, the batteries will connect to a busbar and then from the busbar to the inverter, I would go with the wire for 125a, 1/0 (the manual says 2agw).
Thanks!
Justin