I need a high capacity UPS in the 10-12kW range to keep a rack of servers up while the backup generator starts. I recently purchased an EG4 18KPV hybrid inverter and four EG4 LL server rack batteries. This is grid connected with no solar and no grid back-feed. I am seeing a "glitch" on the critical loads when the mains go off. During the switch-over I can hear the pitch of the server cooling fans change and some computers reboot. Very disappointing.
EG4 uses the term "UPS" in their marketing literature / spec sheets and it has a so-called high speed relay built in gird-to-battery switching. The EG4 specs for the 18KPV say 10ms transfer time which is what most consumer grade 1000-2000 VA UPS are rated for so I fully expected this to work. There is a poorly documented setting on the 18KPV called "seamless switching" which sounds like what I want. I have this checked and yet the glitch remains. Current load is only about 4-5 kW so not even fully loaded, but not nothing either. I may try catching the glitch on an oscilloscope but getting the right capture trigger to see the actual "event" might be tricky.
Interestingly when the critical load is being partly powered by battery, meaning the inverter is already "on", there is no glitch when the mains go off. This "glitch" in output only occurs when load is entirely supplied by the mains and the mains fails causing the relay to switch. So maybe something slow with the inverter turn-on and/or sync? But why do they spec 10ms switching time then?
If found this thread https://diysolarforum.com/threads/online-ups-functionality.53936/ which appears to be focused on using an all-in-one inverter to provide electrical noise isolation like a double conversion UPS. I don't need noise isolation and would rather eliminate double conversion to avoid the resulting efficiency losses. What I need is a simple stand-by battery back-up UPS in the 12kW range that provides 240VAC. Feels like the 18KPV would be perfect. What I am missing?
Is anyone powering sensitive loads like computers directly with an 18KPV? 120 or 240. Without having a purpose made back-up UPS between the inverter and the computers.
EG4 uses the term "UPS" in their marketing literature / spec sheets and it has a so-called high speed relay built in gird-to-battery switching. The EG4 specs for the 18KPV say 10ms transfer time which is what most consumer grade 1000-2000 VA UPS are rated for so I fully expected this to work. There is a poorly documented setting on the 18KPV called "seamless switching" which sounds like what I want. I have this checked and yet the glitch remains. Current load is only about 4-5 kW so not even fully loaded, but not nothing either. I may try catching the glitch on an oscilloscope but getting the right capture trigger to see the actual "event" might be tricky.
Interestingly when the critical load is being partly powered by battery, meaning the inverter is already "on", there is no glitch when the mains go off. This "glitch" in output only occurs when load is entirely supplied by the mains and the mains fails causing the relay to switch. So maybe something slow with the inverter turn-on and/or sync? But why do they spec 10ms switching time then?
If found this thread https://diysolarforum.com/threads/online-ups-functionality.53936/ which appears to be focused on using an all-in-one inverter to provide electrical noise isolation like a double conversion UPS. I don't need noise isolation and would rather eliminate double conversion to avoid the resulting efficiency losses. What I need is a simple stand-by battery back-up UPS in the 12kW range that provides 240VAC. Feels like the 18KPV would be perfect. What I am missing?
Is anyone powering sensitive loads like computers directly with an 18KPV? 120 or 240. Without having a purpose made back-up UPS between the inverter and the computers.