My mini split got a leak, stain on concrete, oil/sticky service ports, almost no cooling. So I tried to recover the refrigerant to a recovery tank using a recovery machine but only got 142g. I was expecting more considering the unit holds 1100g total...maybe like around half.
When I first put my manifold gauge on it showed 123 PSI when the unit was off. Someone mentioned there maybe gas stuck between the 3-way valve and check valve and to run it in heat mode then cool mode with one of the service valves closed to free up the gas for recovery, but this didn't produce anymore recovery. Another mentioned see if there are jumpers to set to put the unit in recovery mode in order to pull out all the refrigerant, or get a service manual. I sent a message to EG4 via there website but have not gotten a reply...wasn't expecting to given their and SS track record.
Anyone have an idea I can try? My concern is, if after I fix the leak, N2 pressure test, vacuum down and refill weighing in the 1100g R410A, if I didn't get all the R410A out to begin with, I could overfill the system and ruin the unit.
When I first put my manifold gauge on it showed 123 PSI when the unit was off. Someone mentioned there maybe gas stuck between the 3-way valve and check valve and to run it in heat mode then cool mode with one of the service valves closed to free up the gas for recovery, but this didn't produce anymore recovery. Another mentioned see if there are jumpers to set to put the unit in recovery mode in order to pull out all the refrigerant, or get a service manual. I sent a message to EG4 via there website but have not gotten a reply...wasn't expecting to given their and SS track record.
Anyone have an idea I can try? My concern is, if after I fix the leak, N2 pressure test, vacuum down and refill weighing in the 1100g R410A, if I didn't get all the R410A out to begin with, I could overfill the system and ruin the unit.