I'd love to get some feedback on my current electrical planning & permit diagram.
Plans are for (30) 400w solar panels with (15) AP Power DS-3 microinverters. A 30 amp breaker can take up to 9 DS-3 micro inverters.
I'd derate the main breaker to 175 and putting in (2) 30 amp breakers.
Do I need to put the (2) 30 amp breakers in the diagram and show the wiring for each breaker from the junction box to the MSP?
Attached is the diagram I currently have.
Plans are for (30) 400w solar panels with (15) AP Power DS-3 microinverters. A 30 amp breaker can take up to 9 DS-3 micro inverters.
I'd derate the main breaker to 175 and putting in (2) 30 amp breakers.
Do I need to put the (2) 30 amp breakers in the diagram and show the wiring for each breaker from the junction box to the MSP?
Attached is the diagram I currently have.