Hello,
I am new to the forum and I recently build a PV system.
It has two inverters in parallel (single phase) SPF 5000 ES with firmware 040 05 701; 041 05 701. Batteries 4xSLA 12V / 24Ah (They are small only to support parallel operation).
I have the following issue. When there isn't enough power from PV modules, the batteries are not charging, not even from grid. I have specified Program 14 to be SNU. The problem is that, if it is a cloudy day, or the load power is more than PV production, the inverters draw 1.6 to 2A from the batteries the whole day without charging. They even drop below specified voltage in Program 21 48.0V. They start charging after sunset. I tried different settings and restarts, but it is still the same.
I only managed to make them charge the batteries the whole day using in Program 1 SOL. But then the panels are not used to supply load if they don't have enough power. And inverters switch internal relays many times a day. Also the charge is starting again below 48V, which is very strange. I don't want the batteries to go below 51.2V. Or said in another way I want them float charge, no cycling.
Is it normal behavior? May be I am missing something in configuration.
Here is my current config:
I am new to the forum and I recently build a PV system.
It has two inverters in parallel (single phase) SPF 5000 ES with firmware 040 05 701; 041 05 701. Batteries 4xSLA 12V / 24Ah (They are small only to support parallel operation).
I have the following issue. When there isn't enough power from PV modules, the batteries are not charging, not even from grid. I have specified Program 14 to be SNU. The problem is that, if it is a cloudy day, or the load power is more than PV production, the inverters draw 1.6 to 2A from the batteries the whole day without charging. They even drop below specified voltage in Program 21 48.0V. They start charging after sunset. I tried different settings and restarts, but it is still the same.
I only managed to make them charge the batteries the whole day using in Program 1 SOL. But then the panels are not used to supply load if they don't have enough power. And inverters switch internal relays many times a day. Also the charge is starting again below 48V, which is very strange. I don't want the batteries to go below 51.2V. Or said in another way I want them float charge, no cycling.
Is it normal behavior? May be I am missing something in configuration.
Here is my current config:
Program | Description | Setting |
01 | Output source priority | SUB |
02 | Maximum charging current | 3A |
03 | AC input voltage range | UPS |
04 | Power saving mode | DIS |
05 | Battery type | USE |
06 | Auto restart when overload occurs | DIS |
07 | Auto restart when over temperature occurs | DIS |
08 | Output voltage | 230V |
09 | Output frequency | 50Hz |
10 | Number of series batteries connected | 4 |
11 | Maximum utility charging current | 2 |
12 | Setting voltage point back to utility source | 51.2 |
13 | Setting voltage point back to battery mode | 54.0 |
14 | Charger source priority | SNU |
15 | Alarm control | ON |
16 | Backlight control | ON |
17 | Beeps while primary source is interrupted | OFF |
18 | Overload bypass | ENA |
19 | C.V. charging voltage | 56.4 |
20 | Floating charging voltage | 54.4 |
21 | Low DC cut-off voltage | 48.0 |
23 | AC output mode | PAL |
28 | Address setting | 1 |
37 | Real time setting---Year | |
38 | Real time setting---Month | |
39 | Real time setting---Date | |
40 | Real time setting---Hour | |
41 | Real time setting---Minute | |
42 | Real time setting---Second | |
43 | Battery equalization | DIS |
44 | Battery equalization voltage | 58.4 |
45 | Battery equalized time | 60 |
46 | Battery equalized timeout | 120 |
47 | Equalization interval | 30 |
48 | Equalization activated immediately | OFF |
49 | Utility charging time | 0000 |
50 | AC output time | 0000 |