Help with string(s) sizing 6000xp

jcollinsks

New Member
Joined
Jul 5, 2023
Messages
28
Location
West Virginia
I got a kit without panels from ss, my plan is to expand to at least one more 6000xp in the future so I went with a pallet of these

I’m a bit confused on the 480 VOC max, in terms of what’s best string sizes especially with their data sheet not including much about the bifacial side.

I was thinking 8s2p but I’m second guessing myself.

Also the docs says it can have more amps but not more voc and optimal voc is 385. With the two moots is it a max of 480voc total or on each also?
 
480Voc per MPPT

17A max usable input current. Those panels are 12.7-13.0, so 2P on a single MPPT means you can't use most of the second string.

22A max Isc. 2P on a single MPPT exceeds that.

Bifacial has no impact on Voc or Vmp. It may affect Isc and Imp.

If you want to max out the one inverter you have, 10S on each MPPT should be fine unless it gets below -40°C/-40°F.

Once you get the second inverter, 9S on each MPPT to use all 36 panels.
 