Here is a simple way to think about off grid solar.
batteries are a surge and reserve energy storage. Solar needs to be sized to handle the watts used during daylight hours.
You need to know watts used per day, and sunlight hours or “solar day hours” for your area. Then you size the array for 1.5 or more times the daily usage so the battery bank can be recharged during the available solar hours.
so, knowing the daily watt usage is#1.
battery bank needs to hold the total daily usage, and have reserve for times when weather doesn’t produce sunlight... for at least a week...
It can be calculated with math.
wattage of operating loads,and runtimes of the loads, added together.
for instance. A 60 watt bulb running 24 hours a day needs (60x24) 1440 watt hours or 1.44KWh of storage minimum. For a 7 day cushion you need 7 times that (1440x7) 10080 watt hours, or 10.08KWh
If you have 5 sun hours in your area, you need (1440/5) 288 watts of solar panels to replace each day of usage with a 7 day cushion, you need (288x7) 2016 watts.