The point here is that you are well under 100A at peak load. At 8kW you are only using 33A. You would have to peak at 24kW to hit 100A and 48kW to hit 200A. This is all great news for you. All you need to do is the simplest installation. Mount the invert next to your main load center and connect as I said above. You don't need a breaker because your meter already has a 200A breaker in it. Your main load center already has a breaker in it too. So that allows you to disconnect your home from the inverter and your inverter from the grid. Since everything is on the wall and nothing is in the wall, the job of connecting the inverter in between the meter and the main load center should be easy. You just need to redirect your existing wire from the main load center to the inverter and then route from the inverter to where the current wire comes into the main load center at the main breaker. Again no need for any breakers. That will give you 200A pass-through to your house through the inverter, and will give you 50A from the inverter as backup power when the grid fails. You can connect your PV sources however you like as well since it is all exposed and looks easy to work with. In addition, if you later desire to add a bypass switch, that is easy too. You just add things as I mentioned. But if that is too expensive, you can just keep a spare SER cable around to bypass the inverter if you need to. If I were in your situation, I would just buy another inverter. It would be less expensive than the bypass. You could either use it as a spare for an emergency, or put it on the wall in parallel with the first one. Then if one fails you still have 50A (12kW of backup power to keep you going until you decide how you want to fix it. The second inverter would be optional for now and you can buy it later if you decide you want it. This is all straightforward.What about your peak usage?
I have a new freezer that is very energy efficient, only 0.55 kWh a day but has 1000 watts peaks when it switches on. The inverter has to provide those peaks as well. 4 freezers would be 4000 watts . On top of 8k you are already maxing out the 12k of the inverter