wildbillpdx
Solar Enthusiast
Before I turn this thing on, I'd like to get some verification and comfort that my system will work and be safe. I think I've got things under control but would really like to be sure.
I'm still installing pieces but here are the components and the plan:
Sanyo PV Panels: HIP-200BA3
Maximum Power Voltage (Vpm) 55.8 volts
Open Circuit Voltage (Voc) 68.7 volts
Maximum Power Current (Ipm) 3.59 amps
Configuration: 6S3P
Voltage: 334.8
VOC: 429 volts
Amps: 10.77
EG4 6000EX AIO
(Maximum PV open voltage) 500 vdc
Max. DC Input current / Total Array Amps 27 amps
Max PV Power 7500 watts
PowGrow Combiner box
4 strings
15 amp fuses
Surge protection
50 amp circuit breaker
Siemens Load Center
40 amp breaker to AIO
30 amp breaker to transfer switch
20 amp breaker for additional outlets
Main Panel
40 amp breaker 8/3 romex to AC-In on AIO
Batteries
EG4 LifePower4 x 3 (48v 100ah)
Battery Cut Off Nader DC Circuit Breaker | 60V 200Amp
PV Cut Off IMO DC Disconnect Rooftop Isolator Switch
AC Cutoff smseace Miniature Circuit Breaker Low Voltage AC 40A 400V 2 Poles DIN Rail Installation DZ47-63 C40
Anything stand out as a problem?
I'm still installing pieces but here are the components and the plan:
Sanyo PV Panels: HIP-200BA3
Maximum Power Voltage (Vpm) 55.8 volts
Open Circuit Voltage (Voc) 68.7 volts
Maximum Power Current (Ipm) 3.59 amps
Configuration: 6S3P
Voltage: 334.8
VOC: 429 volts
Amps: 10.77
EG4 6000EX AIO
(Maximum PV open voltage) 500 vdc
Max. DC Input current / Total Array Amps 27 amps
Max PV Power 7500 watts
PowGrow Combiner box
4 strings
15 amp fuses
Surge protection
50 amp circuit breaker
Siemens Load Center
40 amp breaker to AIO
30 amp breaker to transfer switch
20 amp breaker for additional outlets
Main Panel
40 amp breaker 8/3 romex to AC-In on AIO
Batteries
EG4 LifePower4 x 3 (48v 100ah)
Battery Cut Off Nader DC Circuit Breaker | 60V 200Amp
PV Cut Off IMO DC Disconnect Rooftop Isolator Switch
AC Cutoff smseace Miniature Circuit Breaker Low Voltage AC 40A 400V 2 Poles DIN Rail Installation DZ47-63 C40
Anything stand out as a problem?