Hi DIY Solar Folks,
Thanks to your many helpful posts, I am considering adding solar power to my rural home near Madison, WI.
First I want to consider a minimal system to run a well pump and septic pump, one at a time, during a power outage. I think each requires no more than 10 kW to start and 3 kW to run.
If I use two Victron MultiPlus-II 120V inverters in split-phase:
- For 2x 48/3000/35-50, continuous power is 2x 2400 = 4800 W and peak is 2x 5500 = 11000 W.
- For 2x 48/5000/70-95, continuous power is 2x 4000 = 8000 W and peak is 2x 9000 = 18000 W.
I think I can use 2x 48/3000/35-50 to run my well pump and septic pump, one at a time. Is that true?
If it is false, would 2x 48/5000/70-95 do the job? Or which minimal Victron inverter(s) would do the job?
Thank you.
P.S. Here are details on the pumps.
The well pump is a STA-RITE 10P4E02H-03, 230V, 1 HP, on a 15 A breaker, locked rotor amps (LRA) = 41.8 (says manufacturer, which also said inrush is close to and a little less than LRA; and that starting current is about 4x running current). I think it requires 41.8 A * 230 V = 9614 W to start and about (1/4) * 9614 W = 2404 W to run.
The septic pump is a Gould WE1012H, 230 V, 1 HP, on a 20 A breaker, maximum current: 12.5 A, locked rotor current: 36.2 A. I think it requires 36.2 A * 230 V = 8326 W to start and no more than 12.5 A * 230 V = 2875 W to run. (A cheap clamp meter showed a max of 32.68 A, which more-or-less matches the specified locked rotor current.)
Thanks to your many helpful posts, I am considering adding solar power to my rural home near Madison, WI.
First I want to consider a minimal system to run a well pump and septic pump, one at a time, during a power outage. I think each requires no more than 10 kW to start and 3 kW to run.
If I use two Victron MultiPlus-II 120V inverters in split-phase:
- For 2x 48/3000/35-50, continuous power is 2x 2400 = 4800 W and peak is 2x 5500 = 11000 W.
- For 2x 48/5000/70-95, continuous power is 2x 4000 = 8000 W and peak is 2x 9000 = 18000 W.
I think I can use 2x 48/3000/35-50 to run my well pump and septic pump, one at a time. Is that true?
If it is false, would 2x 48/5000/70-95 do the job? Or which minimal Victron inverter(s) would do the job?
Thank you.
P.S. Here are details on the pumps.
The well pump is a STA-RITE 10P4E02H-03, 230V, 1 HP, on a 15 A breaker, locked rotor amps (LRA) = 41.8 (says manufacturer, which also said inrush is close to and a little less than LRA; and that starting current is about 4x running current). I think it requires 41.8 A * 230 V = 9614 W to start and about (1/4) * 9614 W = 2404 W to run.
The septic pump is a Gould WE1012H, 230 V, 1 HP, on a 20 A breaker, maximum current: 12.5 A, locked rotor current: 36.2 A. I think it requires 36.2 A * 230 V = 8326 W to start and no more than 12.5 A * 230 V = 2875 W to run. (A cheap clamp meter showed a max of 32.68 A, which more-or-less matches the specified locked rotor current.)