Hello! I just applied a new Victron MPPT 250/100 to a 24V bank made of 12x 2v 1000ah batteries.
The operating manual for the batteries does not list a bulk/absorption voltage, but lists 2.35V per cell (28.2V) as absolute max for a 'refresh' charge, and 2.25V per cell (27V) at 77F for float. The manual frequently says never exceed 2.35V (28.2V) per cell.
In entering these values in the VictronConnect app, all charging phases are 0.5-1V over the settings. The batteries are usually around 45F, so I imagine temp compensation might be playing a role.
How can I accurately set the controller so it doesn't exceed the operating manuals absolute max of 28.2 V, while still entering accurate settings? Will temp compensation always put me over - and is it OK to exceed manufacturers recommendations in this case?
Many thanks!