I am guessing he is referring to AC cable from inverter to CU.
First thing though... if you're asking this question you're obviously not a sparky.. but installing a new circuit comes under Building Regs Part-P, so will require a Part-P qualified individual to sign-off, even if you are doing a self install.
I'm not a sparky, but an 8.2kW inverter can deliver up to 36A at UK's nominal 230V. That will require minimum of 6mm^2 T&E cable and a 40A MCB, depending on the cable's temp rating.
6mm^2 T&E should be good for up to 45A (under reference method A / 90C).
But depending on distance you may want to consider a larger diameter cable to minimise losses and minimise voltage drop/rise.
Personally, I'd chose 10mm^2 for the above reasons.