Swapping out

Putting the fuse at the bus bar end avoids this. Ideally you would fuse both ends of the battery wires, but most people don't and depend on the BMS to cut the current.
With my setup (3x 100ah batteries) in 12v configuration and the 2000 watt inverter, what size fuse would you put on each battery between the bus bar? And what size wire would you use from the batteries to the bus bar?
 
With my setup (3x 100ah batteries) in 12v configuration and the 2000 watt inverter, what size fuse would you put on each battery between the bus bar? And what size wire would you use from the batteries to the bus bar?

My opinion -

Each BMS is 100amps max (but can spike higher momentarily, we plan on expected)

This from the windy nation welding wire chart - #6 will do the job with 115amps, but I would do #4 just for extra headroom at 150amps. Note this is a lot smaller than the 2/0 you originally listed because it is welding wire verse.


1714330449829.png


Fuses on battery post and bus bar end of battery wire - both 150amp - Type is MRBF.
If you only put a fuse at one end of the battery cable put it at the bus bar end. In the event of a short across the posts realize you are depending on the battery BMS to act as a fuse and it could just as easy be a short instead of an open. If you fuse at the post and at the bus bar end you are covered for all eventualities.

For the inverter - you are running 2000watts/12.8v = 156amps - I would use #2 wire for this.
You can upsize if you ever think you want to run 3000w in future = 234amps = 1/0 wire.
Note - I skip 1 awg because it isn't a standard size of welding/battery wire. If you move to a THHN or other wire type that is a different ampacity chart.

For the fuse I would use a 200amp class T fuse as close to the bus bar as you can get.

For all fuses - cheaper isn't better - many people recommend blue sea systems, but they are just releabled Eaton, Bussman, or littlefuse with a higher price -So order from someplace like powerex


On all cable ends use rubber boots to cover the bolt heads. The bus bars should be the type with a cover over it or you need to do something to prevent a short between them and everything else.

Big note here - if you don't have a good hydraulic crimper (temco or other quality brand, NOT the $40 off amazon with the funky name) order the cables to length from windy nation with lugs already on them. You can generally get them cheaper direct verse the amazon store.

And don't use the chassis as a negative pole - run the correct size wire for everything. Using a chassis 'ground/negative' is old school from when vehicle lights were first added to cars and they wanted to save a few pennies and not run the second wire. It generally causes nothing but issues when used for that or anything else.

If you have ever chased wires on a vehicle pre-1970 you would know what I mean. Flip the turn signal and both side light up, loose negative to chassis wire. Put a new screw in or clean the connection and now the turn signal is bright. It didn't help that the brake light and turn signal light used a 1157 buld with two filaments in it tied together and in some vehicles they fiddled with the ground to decide which to light up.
 
Last edited:
My opinion -
Thank you. Per your advice, and everyone else's, I have come up with this. The 150a fuses are MRBF, the 200a fuse is class T. I oversized the wire between batteries and bus bar, just to be safe. I also added a disconnect heading to the inverter just so I can shut it off completely if I need to. Any last bit of feedback before I order everything and build this?

Screenshot 2024-04-30 at 12.58.03 PM.png
 
Thank you. Per your advice, and everyone else's, I have come up with this. The 150a fuses are MRBF, the 200a fuse is class T. I oversized the wire between batteries and bus bar, just to be safe. I also added a disconnect heading to the inverter just so I can shut it off completely if I need to. Any last bit of feedback before I order everything and build this?

View attachment 212490


The disconnect lives in the negative line between the bus bar and the shunt. It will work either place, but in general it is done on the negative.
 
Here's what I've built - I'm just waiting for the class T fuse to test everything. I just thought I'd see if anyone has any last minute feedback: https://jmp.sh/4tuiYAmL

This will get installed in the pass through of our trailer, and then I'll also tie in the existing 12v electrical system into this (positive bus bar/shunt).
 
Looks good. Remember to pre charge the inverter before you close the disconnect. A 12 v incandescent bulb will work fine. It dims, you’re done and close the switch. Secure any long cables so they don’t flap around. You can treat the wood with fire resistant spray or use header paint.
 
Remember to pre charge the inverter before you close the disconnect. A 12 v incandescent bulb will work fine. It dims, you’re done and close the switch.

What is the proper way to do this with everything hooked up to the disconnect? I saw Will's video (
) - do I need to what he's showing before I connect the negative on the inverter? What about when I want to toggle the disconnect?
 
I like it, looks good.

One suggestion - turn the switch so the wires feed from the sides - take the strain off the upper cable or secure it to something.

Precharge resistor - only needed when you turn on the system.

I had a little 3" cubic plastic box laying around. So I put a NO (normally open) pushbutton switch, 10 amp fuse with holder, and a 25Ω 30 watt resistor (gold thing in there) all wires in series together. The ends are connected to both sides of the switch. The wires on the switch and fuse holder are 16awg, just used what was there.

The resistor came in a bag with my inverter so I put it to use.

These are the parts to build except the enclosure


So to turn on after it has been off long enough to discharge, about 15 minutes on my inverter, I just push the button, count to 10 slow and the switch on.

If you never turn it off you never need to precharge so you can just use a light bulb, graphite pencil, larger resistor value for more a longer time the once in a while you need to do it.

20240515_155634.jpg20240515_155649.jpg
 
Last edited:
But nothing in a trailer should use the frame as the
negative path for current.

There were three wires connected to the negative terminal of the battery: one went to the other battery, one went to the solar charge controller, and the other is bolted to the frame (photos attached). What changes should I make here? Should I send my 1/0 wire from my shunt to the frame as the previous system did this? If not, what should I do?
IMG_1663.jpegIMG_1658.jpeg
 
Is your solar charge control set for Lifepo4?
I wouldn’t upgrade the wire between your tow vehicle alternator and the new trailer batteries. If that cable is a bit undersized it’ll work like a buffer to protect your alternator by providing some resistance. Lithium batteries really draw power and can overheat your alternator. A DC to DC converter is a better way to limit current draw, control bulk and float voltage. Half or less of your alternator’s current rating is probably safe depending on environment and air flow.
 
There were three wires connected to the negative terminal of the battery: one went to the other battery, one went to the solar charge controller, and the other is bolted to the frame (photos attached). What changes should I make here? Should I send my 1/0 wire from my shunt to the frame as the previous system did this? If not, what should I do?
View attachment 215662View attachment 215663
Clean all of those connections up and hook it back up the way it was. No need to make changes at this point.
 
Clean all of those connections up and hook it back up the way it was. No need to make changes at this point.
Here has been my plan:
  1. The negative had 3 connections to the battery terminal:
    1. One connecting the two batteries (this can be discarded now that I have bus bars)
    2. One going to the solar charge controller (this will now go directly to the negative bus bar)
    3. One going to the frame. I will be replacing this by running a black 1/0 wire from my shunt and connecting it the frame where the previous negative terminal from the previous batteries were connected to the frame. See #1 in the photo below. This will connect to the frame photo in my previous post.
  2. The positive had 3 connections to the battery terminal:
    1. One connecting to the batteries (this can be discarded now that I have bus bars)
    2. One going to the solar charge controller (this will now go directly to the positive bus bar).
    3. One going to a fuse mounted to the frame, which then leads to feed the 12v system of the trailer. I will be running a new wire from my positive bus bar to this fuse (see #2 in the photo below). This should feed the 12v system.
I'm pretty sure this is all correct in order to tie my new system into the existing system, but can you please confirm?

Edited to add existing solar charge controller to diagram.

Screenshot 2024-05-16 at 6.30.32 AM.png 2024-05-16 at 6.32.03 AM.png
 
Last edited:
Also one last question, unrelated to the previous post. Here's a run through on where I plan to place and mount the battery box - it is on the other side of our heater. Is this OK? https://jmp.sh/DWRk4zaH - would it help if I added some foam insulation on the back side of my battery box? Any thoughts or input?
 
Last edited:
Here's my final build. It turned out really nice. It's super clean, I'm really happy with it. Thanks for all the help! I decided to not place it against the heater and I mounted it across the pass through. The existing 12v system in the trailer is working great (😅). I have not hooked up the inverter yet, I wanted to get a full understanding of the process. I've watched Will's video a few times, and I think I have a good understanding, but can anyone let me know if there's anything correct in the following (or if you have any additional feedback)?

I'm assuming I need to have my disconnect going to my inverter turned on before I start the precharge process. I connect my positive wire to the inverter first. Then I attach a resister to the negative wire and touch that to the inverter for a few seconds. The capacitors are then pre-charged and I am good to hook up the inverter. As long as I leave my inverter connected and the disconnect turned on, I don't need to do anything. If I turn the disconnect off for any reason, then I will need to pre-charge the inverter again before I turn it back on. If I need to disconnect the inverter for any reason, then I'll to discharge the capacitors, by disconnecting the negative terminal, attaching a resistor then touching the positive terminal for a few seconds. Does this all sound correct?

Screenshot 2024-05-26 at 7.30.51 PM.pngScreenshot 2024-05-26 at 7.30.46 PM.pngsdf
 
More or less, but it can take minutes or longer for it to discharge the caps. There should be a bleed resistor inside the inverter that will slowly drain the caps.
 
I don’t have my solar installed yet, and I’m pretty sure the converter installed on my trailer doesn’t support lithium. I have an ac adapter charger that I purchased from the battery manufacturer that clips directly onto the battery terminals. What is the best way to go about charging them manually with my updated system (bus bars and not)?
 