diy solar

diy solar

What Class T fuse for my Ruixus ?

GregM

New Member
Joined
Nov 14, 2023
Messages
110
Location
Datil, NM
Just bought 6 Ruixu (48v) batteries in their cart.
What class T fuse should I get for that system?
 
Tell us more about your system. It is 48 Volt so I assume the only thing hooked to the batteries is the inverter (with integrated chargers).

Typically, with this setup, the max load current will be larger than the max charge current, so we need to calculate the max load current.

Start with the size of the inverter. (I will assume it is a 6000W inverter. The actual wattage of your inverter can be substituted in the calculations.). The max current draw will be when the battery is low so I will use 48V for the voltage. Using Ohm's law we see that the current will be 6000W/48V = 125A.

A fuse should be sized for 125% of the max continuous current so the fuse should be 125A * 1.25 = 156A. This would round up to 175A for the next available fuse size.
Note: You could probably get away with a 150A fuse if you don't expect to max out your inverter, but you risk nuisance trips.

Using the NEC ampacity chart, the wire should be sized to handle the max fuse size.

1708110791042.png

We can see from the chart that it would be a 2/0 wire.
 
The inverter is an EG4 18kpv
The house has a 200a panel.

From the panels....
mppt one 328v 10.92a
mppt two 328v 10.92a
mppt three 328v 10.92a
mppst four 328v 10.92a
 
The 18Kpv is a 12KW inverter.

Going through the numbers gives a continuous fuse size of 312A. I would have 2 2/0 wires each with it's own 150A fuse. The 18K pv has two positive and two negative battery lugs so it is reasonably easy to do it this way.
 
I bought 10' of 4/0 welding cable for the battery to inverter run, a while back.
I'd like to save the second set of DC inputs for future additional batteries if possible.
Boy batteries are expensive.
 
We can see from the chart that it would be a 2/0 wire.
I am adding the same Riuxu batteries with cart and am shopping for 15ft. of wire to connect to a 600 amp busbar that feeds two EG4 3k watt inverters. Windy Nation has a chart that says their 4guage wire will handle up to 160 amps. Would it then be to code? And secondly, I currently have four EG4100AH batteries hooked to the busbar and that same 4guage wire to the inverters. Will I need to upgrade that wire?IMG20240217111136 (2).jpg
 
Last edited:
I found this fuse-block/fuse at Amazon.
Would it be ok with a single run of 4/0?
Had those as well. They might be perfectly fine. However after comparing these fuses with other class-t fuses, I replaced them.

The fuse block and the fuses themselves are just a world of difference compared to other class-t fuses and blocks.

These ones are small and flimsy.
 
Had those as well. They might be perfectly fine. However after comparing these fuses with other class-t fuses, I replaced them.

The fuse block and the fuses themselves are just a world of difference compared to other class-t fuses and blocks.

These ones are small and flimsy.

What did you replace them with?
 
I am adding the same Riuxu batteries with cart and am shopping for 15ft. of wire to connect to a 600 amp busbar that feeds two EG4 3k watt inverters. Windy Nation has a chart that says their 4guage wire will handle up to 160 amps. Would it then be to code? And secondly, I currently have four EG4100AH batteries hooked to the busbar and that same 4guage wire to the inverters. Will I need to upgrade that wire?View attachment 196269

Take a look at these guys....
Wire and Cable Your Way
 
Take a look at these guys....
Wire and Cable Your Way
I decided to go with Windy Nation. They sell the cable in 3' increments if you get the ends installed, which since I don't own a tool for that, seems the prudent approach. Also no shipping cost. They also sell a ANL 200 AMP Fuse, which is better than the Chinese ones on amazon. Their cable is flexible, and the specs are to high standards, with competitive pricing.
 
Last edited:
Windy Nation has a chart that says their 4guage wire will handle up to 160 amps. Would it then be to code?
I will assume you are in the US and need to comply with the NEC code.
1708214619632.png
As you can see, even 90c rated wire does not go anywhere near 150A

So how did they come up with 150A? I suspect it was from ABYC. The American Boat and Yacht Council uses a much more permissive ampacity chart.
1708214948588.png
 
Back
Top