Hello,

First time posting here. I Amin the process of planning out Solar / Battery / Backup system for my single family home. Currently looking at approximately 7.2 KWPV with an additional 10-15 kWh batteries. System will be all Enphase iq8M and 2, maybe 3 IQ5P batteries. What I can't seem to find a good answer on is my interconnection to the main panel. I have a 200Amp main/meter combo that feeds a 100 Amp sub panel and a 70 Amp sub panel, plus a few misc breakers in the main.
The Main 200 Amp panel has 200 Amp bus and is center fed. Question. For breaker sizing from combiner box to panel, I believe I will need a 60 Amp breaker? Can I place that at the far end of the panel? In my case the top most part of panel? Do I need to derate the main panel breaker to 175 Amps for the 120 rule? I also plan on adding a 50Amp car charger as well. Still planning the system, for which would take any recs as well.
Thanks so much.

I have attached some pics. Main_panel_open.jpegIMG_9485.jpegkitchen_sub.jpeggarage_sub.jpeg
 

Attachments

  • main_panel_front.jpeg
    main_panel_front.jpeg
    291.8 KB · Views: 1
If your main panel is a standard model with 200A bus bars then the panel would be limited to a 40A solar breaker. Many new Solar Ready panels are set up with 225A bus bars and a 200A Main Breaker which would allow for up to a 70A Solar Breaker.
 
If your main panel is a standard model with 200A bus bars then the panel would be limited to a 40A solar breaker. Many new Solar Ready panels are set up with 225A bus bars and a 200A Main Breaker which would allow for up to a 70A Solar Breaker.
If I were to replace the main 200Amp breaker with a 175 Amp, in theory I could then add a 60 Amp breaker and still be under the 120% rule.
If I am able to do that it still seems like 175Amps would be fine plenty for my 1900 sq foot house.
Last question. Can you even add a back feed breaker on a panel that has the main breaker in the center like mine as opposed to the opposite end on an end fed panel?
 
If I am able to do that it still seems like 175Amps would be fine plenty for my 1900 sq foot house.
There is a calculation based on a number of factors like sq ft, # kit circuits, large appliances like range and A/C to determine minimum size electrical service.
Here is an online calculator I found.

Last question. Can you even add a back feed breaker on a panel that has the main breaker in the center like mine as opposed to the opposite end on an end fed panel?
Don't know the answer.
 
Last question. Can you even add a back feed breaker on a panel that has the main breaker in the center like mine as opposed to the opposite end on an end fed panel?
I believe this has been clarified in recent code. It’s a common question.

I don’t know the answer off hand.

Of course you can add backfeed, the question is calculation

Look in 705.12 or mikeholt forum search
 