Max pv voltage is 145v for that built in mppt
"Max DC voltage 270 V"
Plenty of headroom there.
Bridge rectifier, 100A. Maybe heatsinked to box. Probably not a problem for the current. But I don't see the point to using it.
That would certainly explain things. But the chart says MPPT range up to 145V. Max 270V.
Are the strings still putting out 160V WHILE you get next to nothing at the inverter?
If so, there is an open circuit. use volt meter to find out where 158V is being dropped.
But if the strings drop from 160V to 2V when breaker closed, then there is a short (likely at the inverter.
Um, no. First, there’s no ‘fuse in the inverter’ that, if blown, would cause the MPPT input to be shorted out.So if the mppt shorted, will it be as simple as replacing a fuse in the inverter?
IF voltage exceeded the max input for the mppt. Unfortunately it may be toast. This is generally a never exceed value.So if the mppt shorted, will it be as simple as replacing a fuse in the inverter?
So get rid of the mds and get bus barsThis photo gives you a basic idea of how it should be wired using the components you have. View attachment 213925
Entire system was designed by an "engineer " in China, sold as a turn key system. So I guess I should be reaching out to them before I void the warranty opening up the inverter. Thanks for the help.IF voltage exceeded the max input for the mppt. Unfortunately it may be toast. This is generally a never exceed value.
As a bandaid, you may be able to use a stand alone mppt to your batteries if your inverter functions normally from the batteries. You just dont have a "built in" CC anymore.
To be clear, Im not recommending that you open up the inverter to fix anything. If your charge controller is indeed damaged, one option is simply using a stand alone, separate charge controller to charge your batteries and abandon the built in one, assuming the rest of the inverter is ok.So get rid of the mds and get bus bars
Entire system was designed by an "engineer " in China, sold as a turn key system. So I guess I should be reaching out to them before I void the warranty opening up the inverter. Thanks for the help.
This is the pdf download spec sheet. Max pv open circuit voltage says 145?
Im not seeing 270 for DC? Thats max AC input i think.
View attachment 213923
Most likely yes.If I disconnect the pv in from the inverter and the lines read 2v still, would that not mean the issue was in the combiner box, not the inverter, and that not enough power is making it to the inverter for it to recognize input?
Looks like I'm not that lucky, is the internal charge controllerMost likely yes.
ShootLooks like I'm not that lucky, is the internal charge controller
Thanks for all your help though.Shoot
You'd think there would be a circuit breaker on the pv input like the ac in and out. Guess I'm off to find one that can handle upto 175v pv max inputThanks for all your help though.
Circuit breakers only control current, not voltage.You'd think there would be a circuit breaker on the pv input like the ac in and out. Guess I'm off to find one that can handle upto 175v pv max input
But if the inverters max pv input is 145vdc I don't get why it was functioning at 160vdc for weeks.