EG4 6000ex unexpected grid surge

wildbillpdx

Solar Enthusiast
Joined
Jun 24, 2023
Messages
396
Location
Oregon
I'm running an EG4 6000ex with three EG4 LifePower4 batteries (48v). The batteries are fully charged and I'm getting some solar production. The inverter is running in Solar/Battery/Utility mode so power should come from solar then batteries. But twice today there was a usage spike that resulted in a grid feed that shouldn't have taken place. Looking for ideas.
 

Attachments

  • Screenshot 2024-01-15 at 14-52-37 SolarAssistant.png
    Screenshot 2024-01-15 at 14-52-37 SolarAssistant.png
    150.4 KB · Views: 9
Yes...I think I do. But is the data showing an overload? It didn't seem to be.
No, no overload, well there could be a few millisecond overload depending on what you are trying to start.
I'd say it's a quirk of the LVX6048, TP6048, EG4 6000EX, maybe more.
I had noticed graphs very similar to yours when my well pump would kick on, I disabled overload bypass and the problem went away.
 