Is it an option to run 2 6000xp's to the input of a 100a sub panel main feed, instead of running to 2 sperate breakers since the load is already protected by the load breaker already in the unit?
Is it an option to run 2 6000xp's to the input of a 100a sub panel main feed, instead of running to 2 sperate breakers since the load is already protected by the load breaker already in the unit?
you cannot put 2 conductors into a single lug of the main feed, so that is why the use of separate breakers to combine them into a single out going conductor
you cannot put 2 conductors into a single lug of the main feed, so that is why the use of separate breakers to combine them into a single out going conductor