Made in North Pole
Off-grid Addict
- Joined
- Feb 8, 2021
- Messages
- 99
Are you aware Batrius is not exactly 1 BMS for multiple parallel banks?because you need one BMS per bank, it may be that a cell on one bank gets a short circuit or simply slowly discharges towards 0V due to dentriden. if so, the other banks charge the remaining cells of the defective bank above 3.65V, it doesn't have to be such high currents, it already smells like 20A per bank, with 6 banks that's 120A so approx. 6kW that have to go somewhere.... you can't solve something like this with a fuse. each bank needs a BMS that is set as low as possible with the charging/discharging power. I have fused my banks with 100A and limited the respective BMS to 50A power, which is enough for 3x Multiplus 2 3000
There is a supervisor: Watchmon Core.
There are K9s: The actual BMS.
For instance, If you have six parallel banks, you need six K9s and one Watchmon Core. The six K9s talk to the supervisor over CAN, reporting battery parameters.
This BMS design uses contractors to control the system. You can have contactors between each bank so you can disconnect the faulty bank in a critical event. There is no chance any cell can be charged over 3.65V except when your contactors fail closed.
Which do you think has the higher chance of failing closed? FET or NO contactor?
Last edited: