Ummm, pretty certain that’s exactly wrong:I don't think the multiplus ii 120x2 has ul listing though, too bad.
Ummm, pretty certain that’s exactly wrong:I don't think the multiplus ii 120x2 has ul listing though, too bad.
My apologies, for multiplus' I look for UL1741 as I plan on using it on a building, not a car/boat.Ummm, pretty certain that’s exactly wrong:
I thought I read that the goodwe can’t use battery to supply loads in the main panel when operating as a grid tie inverter? I’m trying to remember where I read itgoodwe 5048d-es has adjustable export that can be set to zero (measured via CT in main panel), and supports loads on the grid side from battery (also quite cheap, I picked it up for $1800 AUD) I have one working at the moment with a 204ah pack, and aside from the charging settings being fairly clunky (working without a BMS that can talk to the inverter) it has been working pretty well.
Clearly supports Zero Export to CT with an external meter, but seems to only be single phase 230/240VAC.goodwe 5048d-es has adjustable export that can be set to zero (measured via CT in main panel), and supports loads on the grid side from battery (also quite cheap, I picked it up for $1800 AUD) I have one working at the moment with a 204ah pack, and aside from the charging settings being fairly clunky (working without a BMS that can talk to the inverter) it has been working pretty well.
no issues with that here, I have it running in the default mode (grid use minimisation) so PV first supplies the load, excess goes to the battery, further excess goes to export (which I have limited @ 3.6kw). When the sun goes down the battery supplies the loads (or during the day when load>PV generation), then once the battery runs out (or hits SOC discharge limit anyway), it goes back to the grid. I don't actually have anything connected to the back up supply on the inverter at this stage either!I thought I read that the goodwe can’t use battery to supply loads in the main panel when operating as a grid tie inverter? I’m trying to remember where I read it
Nice!no issues with that here, I have it running in the default mode (grid use minimisation) so PV first supplies the load, excess goes to the battery, further excess goes to export (which I have limited @ 3.6kw). When the sun goes down the battery supplies the loads (or during the day when load>PV generation), then once the battery runs out (or hits SOC discharge limit anyway), it goes back to the grid. I don't actually have anything connected to the back up supply on the inverter at this stage either!
Yes, correct.By specifying 'Zero Export to CT capability' I assume you are speaking about an external CT sensor that allows you to export to main input AC panel loads and still keep any inverter current export from leaking back into external grid.
This remote CT sensors adds another level of feature beyond just zero export.
There are more inverters that will prevent export from their AC input port,
Yes, I understand that hybrid inverters that use an internal CT sensor to prevent energy export out into their AC input port are a dime a dozen (most common architecture).with internal AC input CT sensor, than ones that have the remote CT sensor to allow export to supplement local loads and still block export to external grid.
Zero export to CT is poorly worded. You are not sending anything to the CT. You use a CT to measure current direction and strength. Zero export to grid can be achieved by not being in parallel. Grid tied with limiter is about the most accurate identification. You limit generated AC output from your system to that of your house loads. It is not in any way similar to battery charging.I think ‘Zero Export to CT’ is pretty clear.
Yes, Zero Export to CT implies that you are grid-tied and outputting energy that is matching phase and frequency with grid (on both L1 and L2).
In addition, ‘Zero Export to CT’ implies you are exporting energy towards the grid but not enough export and power past the CT sensor that is limiting export.
The analogy I find more helpful is that if a DC-coupled array charging a battery through an SCC.
As the battery approaches full charge, the MPPT will throttle-back PV power to exactly match constant-voltage battery charge power.
If additional loads draw more DC energy from the battery, the MPPT will draw more power from the solar panels to supply that additional DC load.
Zero Export to CT is similar except that the approach of consumption where the CT is placed approaching Zero Amps plays the role of a battery approaching full charge state in the DC-coupled analogy and the inverters ability to throttle-back input to avoid Export past the CT sensor plays the role of the MPPT in the DC-coupled analogy.
No, the solar and the charging are not required. What is required is the ability of a DC-powered (battery and/or SCC) inverter to throttle-back grid-tied power generation to avoid export past an external CT sensor clamped to the same leg.
Not understanding how that is relevant, but if you want yo provide a link, I’m happy to have a look…
The Zero Export to CT capability I’m discussing is no different than what any Solark Hybrid inverter can deliver (as well as the Schneider Conext XW Pro).
I beg to differ. You are exporting power towards the CT (but not enough to export past it).Zero export to CT is poorly worded. You are not sending anything to the CT.
CorrectYou use a CT to measure current direction and strength.
Agreed, but so what?Zero export to grid can be achieved by not being in parallel.
I’ve used GTIL (and still do) but no one understands it. Since Solark started using ‘Zero Export to CT’ I’ve decided that is a much better and easier-to-understand term for the capability (precisely because the exported power is being pushed out towards the CT but prevented from exporting past it).Grid tied with limiter is about the most accurate identification.
My point was that from a control point of view the throttling of power generation is similar. In the case of DC-coupled battery charging, the SCC detecting that the battery is approaching full and switching to CV mode translates to higher string voltage to throttle-back PV power generation.You limit generated AC output from your system to that of your house loads. It is not in any way similar to battery charging.
Agree. But at this point the entire industry has adopted ‘coupled’ and it also suggests interface/connection and communication in ways that ‘parallel’ cannot.The word coupled is tossed about too often when the word parallel should be used. A MPPT SCC is in parallel with the battery.
The problem is that you are not preventing power from being exported back to grid. You are just trying to match loads that your house has and not exceed them. Exceeding them means export. Sudden load drop on the grid side can also mean export...
I’ve used GTIL (and still do) but no one understands it. Since Solark started using ‘Zero Export to CT’ I’ve decided that is a much better and easier-to-understand term for the capability (precisely because the exported power is being pushed out towards the CT but prevented from exporting past it).
...
I think the term "Zero Export Past CT" would be a better expression, implying that the CT is like a gate beyond which it shall not pass. Ignore the fact that the CT can't actually block anything if it wanted to.I’ve used GTIL (and still do) but no one understands it. Since Solark started using ‘Zero Export to CT’ I’ve decided that is a much better and easier-to-understand term for the capability (precisely because the exported power is being pushed out towards the CT but prevented from exporting past it).
Ahhh, you’re talking about the distinction between ‘True Zero Export’ and ‘Pseudo Zero Export’…The problem is that you are not preventing power from being exported back to grid. You are just trying to match loads that your house has and not exceed them. Exceeding them means export. Sudden load drop on the grid side can also mean export.
Agree.From the grid side of things it is loads carried by generation. The supply does not discriminate with which loads it powers it just raises and lowers output based on total. When you parallel with it and pick up load you can pretend it is just your house loads you pick up but the grid does not know this because it is still connected but seeing less demand.
And I agree with all of this as well though you are kind of preaching to the choir since I was one of the first to start a number of threads on Grid Tie Inverter Limited which few were interested in or responded to.Straight grid tie relies on the fact that the grid always has loads to pick up unless grid goes down. Limited grid tie is simply supplying enough to cover partially or entirely what otherwise would be your loading on the grid.
‘Thou Shall Not Pass’ - I like it!I think the term "Zero Export Past CT" would be a better expression, implying that the CT is like a gate beyond which it shall not pass. Ignore the fact that the CT can't actually block anything if it wanted to.
Sorry about that....
And I agree with all of this as well though you are kind of preaching to the choir ...
SW will not export but it does have a generator assist function that will effectively work as a peak load shaver if you’re running from a grid source vs. the generator. I’ll say that’s as close as you’ll ever come to getting the functionality you‘re looking for in 24V. Curious: why are you putting a 24VDC condition on the system? You’ll benefit from going to 48V in choice, performance and flexibility.From what I’ve understood, the SW will not export AC power Into the AC input (offsets loads onAC output only).
The XW Pro apparently will (using an external energy meter that communicates with it) but it’s more complex to get set up than in on inverters such as Solark with inputs for exterbal CR sensors…